Posted: 2020-07-04 03:34 AM
This question was originally posted on DCIM Support by Chu Li Wei on 2018-01-11
Hi Team ,
We used DCO 8.1 to our customer , for power calculation , I not yet put the IT assits to rack and
only connect to rPDU from DCE , my question is why it still have estimate load on DCO before
put the IT assits to rack ? How to calculate on it ? Your advice would be appreciated .
Best Regards
(CID:128061168)
Posted: 2020-07-04 03:34 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2018-01-11
Hi Chu Li,
It seems the illustrated rack contains power measurements, so the estimated load calculations would always full back to the best available information in the rack. For detail detail description please see this page: Adjusted nameplate or predicted power
So in your illustrated example, the estimated load calculations and predictions are based on the measurements. The capacity calculations would display your expected estimated load as soon as you add a device/server (to this empty rack) and connect to the rack pdu's.
Kind regards
(CID:128061182)
Posted: 2020-07-04 03:34 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.