Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

How many NetBotz 750 devices does the "SWDCEVMACT-DIGI" license cover?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How many NetBotz 750 devices does the "SWDCEVMACT-DIGI" license cover?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
itaktau
Crewman itaktau
Crewman

Posted: ‎2025-04-08 10:23 PM

0 Likes
4
720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 10:23 PM

How many NetBotz 750 devices does the "SWDCEVMACT-DIGI" license cover?

Good day!

We have 5 offices in different parts of the city. In the head office we bought a NetBotz 750 device with sensors, cameras and a "SWDCEVMACT-DIGI" license. Now the question: if we buy NetBotz 750 devices for the remaining offices, do we need to buy this license again for each office or is the already purchased "SWDCEVMACT-DIGI" license enough to cover all our 5 offices?

 

Thx.

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • EcoStruxure IT Data Center Expert
  • english
  • netbotz
  • Netbotz 750
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2025-04-09 05:53 AM . Last Modified: ‎2025-04-09 05:54 AM

1 Like
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-09 05:53 AM . Last Modified: ‎2025-04-09 05:54 AM

Hello @itaktau,

 

The SWDCEVMACT-DIGI is the activation license for an EcoStruxure IT Data Center Expert appliance.  The activation license enables the server to discover 25 nodes and the server comes with 1 surveillance node.  A surveillance license is needed for each camera that you wish to monitor / record motion for in Data Center Expert.

 

The 25 node license that gets enabled with the VM Activation allows you to discover up to 25 devices.  In your case if you only have NetBotz 750's, it would allow you to discover and monitor via SNMP up to 25 of them.

 

If each NetBotz appliance has 1 or more cameras, you will need to obtain a Surveillance license for each camera.  If a NetBotz appliance has 4 cameras, you will need 4 surveillance nodes for that specific NetBotz appliance setup.  If needed, you can find surveillance SKUs on apc.com: https://www.apc.com/us/en/search/?q=surveillance+node+digital&submit=Search

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

itaktau
Crewman itaktau
Crewman

Posted: ‎2025-04-09 08:40 PM

0 Likes
0
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-09 08:40 PM

Cory, thanks for the detailed answer. It turns out that if we have, for example, 4 cameras in the head office (the maximum supported number for our device), then our head office requires 5 licenses (1 + 4). And if the other offices have exactly the same configuration of NetBotz 750 + 4 cameras, then in principle this one license is enough for us to cover all devices in all offices, right? Or in addition to cameras, also temperature, humidity sensors, etc. also use up licenses?

 

Thx.

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2025-04-10 04:48 AM

0 Likes
1
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-10 04:48 AM

Hi @itaktau ,

As Cory mentioned, the regular licenses support the devices themselves. If you have 2 NetBotz, you will use up 2 licenses. As for the cameras, DCE will only capture images from those cameras using surveillance licenses. Again, Cory mentioned that DCE has 1 by default.

If you have 2 NetBotz and a total of 8 cameras, you need 2 regular licenses (covered by the default 25 nodes) and you will need 8 surveillance licenses if you want DCE to capture those images. There is only 1 by default so you need 7 more. I believe the smallest surveillance license number is 10 nodes:
https://www.se.com/us/en/product/SWDCE10NSV-DIGI/license-ecostruxure-it-data-center-expert-digital-p...

Thanks,

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

itaktau
Crewman itaktau
Crewman

Posted: ‎2025-04-10 08:51 PM

In response to APC_Steve
0 Likes
0
633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-10 08:51 PM

Hi Steve, thanks for the detailed answer.

 

Now we understand how the licenses work and that we need to buy 7 more licenses or more if we want to use more cameras.

 

Thank you guys so much for taking the time to answer our questions.

Have a great day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore