How long can I extend the utp cat5 cable to connect to leak rope NBES0308

Dear All,

 

How long can I extend the utp cat5 cable to connect NetBotz 750 to leak rope NBES0308 ?

 

Best Regars,

Nathawat

Tags (1)
1 Reply 1
APC_Steve
Commander Commander
Commander
0 Likes
0
140

Re: How long can I extend the utp cat5 cable to connect to leak rope NBES0308

Hi @sesa328748_brid 

 

Max length is 100 feet.

If you have 20 feet of leak cable, you can use 80 feet of Cat5.

If you have 20 feet of leak cable, you can use 60 feet of Cat5.

And so on.


Thanks,

Steve