How do i set up daily humidity/temp reports

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How do i set up daily humidity/temp reports
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

0 Likes
4
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

How do i set up daily humidity/temp reports

How do i set up daily humidity/temp reports to be emailed to a group? 

(CID:146669911)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

0 Likes
2
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

Hello Mr Muro,

Scheduling a Report to Export Data

1) Open the Data Center Expert Client and navigate into the Reports perspective.

2) Create a new report or run a saved report and select Edit Report Criteria icon in the upper-right of the report.

3) You can schedule the report to run on a regular basis in the left pane under Name and Schedule Data Export.

4) Select the checkbox for Enable Export.
 
5) For the Export name option, select Add Export...
 
6) Select a type for the export and select Next.
 
7) Fill in the necessary details for the export and then select test-export and a test file should be sent to the destination system.  Select Finish.
 
😎 Change the Delimiter and Locale if necessary and then choose the Scheduling for the report to be automatically exported.
 
9) Select the Report Interval, which by default will contain all available data.
 
10) Select OK and the report will be generated and scheduled to run on a basis that was defined.
 
NOTE: Data Center Expert will only export data as a text file using the delimiter that was defined in the Name and Schedule Data Export settings.
I also written a tip on how to generate reports in DCE which may be useful for you. You can access it here.
There is also a K-base available: https://www.apc.com/om/en/faqs/FA301697/
 
I hope this helps. 
Regards,
Bala

(CID:146669919)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

In response to DCIM_Support
0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

I'm able to generate the report.. However the zip file does not open as a graph. 

They need to see a graph

(CID:146670004)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

In response to DCIM_Support
0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2024-04-03 01:13 AM

Scheduled reports only include raw data, no graphs.  There is no current way to have graphs in scheduled reports.

(CID:146670009)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2023-10-22 02:22 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:26 PM . Last Modified: ‎2023-10-22 02:22 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of