Hi,
Kindly can someone tell me how many PODs 150 I can cascade on the 250 and after which number I need to add a power supply AP9505i ?
Thank you All
(CID:148342174)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM
This answer was originally posted on DCIM Support by Gianluca Bertuletti on 2019-08-22
hi
usually i add a power supply if i have more than 8 pods
(CID:148342240)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM
This answer was originally posted on DCIM Support by Gianluca Bertuletti on 2019-08-22
Hi
page 10 of manual
(CID:148342232)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM
This answer was originally posted on DCIM Support by mark keserwany on 2019-08-22
Thank you for response, i ended up reading that after posting my question but my doubt is still about the power supply since it is mentioned u can add one but it is not clear if it is mandatory
(CID:148342235)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM
This comment was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-08-22
Dear Mark,
I noticed the following information in the Netbotz Compatibility matrix.
requiring one AP9505i power supply for every fourth pod
https://www.schneider-electric.com/en/download/document/APC_JHIN-7PTK7P_EN/
(CID:148342282)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM
This answer was originally posted on DCIM Support by Gianluca Bertuletti on 2019-08-22
hi
usually i add a power supply if i have more than 8 pods
(CID:148342240)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM
This comment was originally posted on DCIM Support by mark keserwany on 2019-08-22
Thank you for that information
(CID:148342244)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:43 PM . Last Modified: 2023-10-22 02:06 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.