Floor tile airflows did not add up to downflow CRAC airflows

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Floor tile airflows did not add up to downflow CRAC airflows
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

0 Likes
8
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Floor tile airflows did not add up to downflow CRAC airflows

Hello guys,

I ran into a bit of a problem..
First of all in my Data Center i have few hot aisle containment pods, and we have inrow's for cooling.

After the placement of the racks and the inrows in a closed aisle I can see in the cooling tab that all racks are green - they all getting enough cooling.
I have yet to install my temperature sensor so i want to see the calculated map in the 3D veiw model.
When i try to see it, it throws me this message "Floor tile airflows did not add up to downflow CRAC airflows


I've read in other threads that this happens when you use non apc inrow, and so I changed it and placed an apc ones instead and still, i get this Error message..

Could you please help me to find the solution to this?

Thank you,
Gleb Tyunikov

(CID:134024383)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • bug
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

0 Likes
4
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Hi Gleb,

As illustrated in the following image, I have used one "InRow RC 300mm Standard" unit without any problem:

I think to understand your issue, I would need more details about the setup - can you provide a copy of your backup file (shared safely with me)?

Kind regards

(CID:134024443)

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Hi Gleb,

Can you please share screen captures illustrating which cooling units/part numbers (from Genome Library) you are using, thanks.

Kind regards

(CID:134024422)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Hi jeff,

Unfortunately i cant share  a screenshot
But I'm using the APC 300mm standard units

Thank you

(CID:134024428)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

0 Likes
4
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Hi Gleb,

As illustrated in the following image, I have used one "InRow RC 300mm Standard" unit without any problem:

I think to understand your issue, I would need more details about the setup - can you provide a copy of your backup file (shared safely with me)?

Kind regards

(CID:134024443)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

In response to DCIM_Support
0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Well as i said earlier its not possible to share any screenshots or backup files..

But I will be more than happy to provide you with specific technical information...

What is strange to me in my situation is that in the cooling tab i can see that the racks are getting cooled and are using right temperatures and only the 3D representation wouldn't work..

When the InRow is placed, is there any specific information that has to stay written on it? like in your picture the "manufacturer" "model" any else?  

(CID:134024456)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

In response to DCIM_Support
0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Hi Gleb,

I was able to reproduce:

As illustrated, if I customize a copy of my InRow cooling unit (by replacing APC with another manufacture) in my Genomes. And then drag this to the floor and run 3D temp calculations, then I see a similar notification as you've mentioned:

I will capture a bug report for this.

 

Workaround:

If I use the InRow cooling unit (without modification) and drag it to the floor:

And then change the manufacture name for this unit on the floor:

Now I can run the 3D temperate simulation without any problem:

Kind regards

(CID:134024488)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

In response to DCIM_Support
0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:27 PM . Last Modified: ‎2024-04-04 03:20 AM

Amazing,

Thank you very much Jeff

have a great day!

(CID:134024496)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:28 PM . Last Modified: ‎2024-04-04 03:20 AM

In response to DCIM_Support
0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:28 PM . Last Modified: ‎2024-04-04 03:20 AM

You are most welcome, Gleb

have a great day, too

thanks.

Kind regards

(CID:134024499)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:28 PM . Last Modified: ‎2023-10-22 02:06 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:28 PM . Last Modified: ‎2023-10-22 02:06 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of