Errors in Rack PDU readings?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Errors in Rack PDU readings?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

0 Likes
4
718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

Errors in Rack PDU readings?

I have noticed on a couple of 3 phase Rack PDU's figures similar to the ones show in the attached image

Basically Phase 3 and Bank6 Current are both 1.3A @ 242V which equates to 315W (VA)

Total PDU Power and Phase 3 Power both read 240W whilst Bank 6 reads 315W. Shouldn't these all be reading 315W?

What is going on here?

I have no way to measure power factor of the load but it looks like the PDU's might be taking into account power factor for the 240W readings but not for the 315W reading.  A load PF of 0.76 would account for this but it does not make sense that you should have 3 Real Power readings (W) that should be the same with different values.

Can this be corrected?

My theory above presumes the PDU can measure Power Factor, so why does Power Factor not get displayed in DCE?  It would be better to see PF in DCE if it is measured.

 

Edit:  The PDU is an AP8886

I just noticed that this is DCE 7.2.6 and that DCE 7.4.0 has a later version of DDF which does seem to return Power Factor, at least it does on an AP7953.  However it always reads 1.0, suggesting the PDU Gen 1 does not measure PF but assumes the PF to be 1.0 as well as the voltage assumed to be 230V?

 

(CID:108827415)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

0 Likes
2
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

Hey Garry,

 

If the customer is concerned about this and you can not do it, ask them to run the SNMPwalk of this device. The walk on the device is the only way to know for sure if these values are from the device or calculated in any way on the DDF. Please get the firmware rev of the device also as potentially if this is a device issue, it may be different in a different firmware.

 

As for the DDF version, they are updated regularly and I would expect a newer version of DCE to have a newer DDF. Since this is all in watts however (or listed in the image as such) neither the power on phase 3 or bank 6 should be changed by any power factor as they are both showing in watts and not VA. This again could be a DDF formatting issue but we need the data to be sure. 

Also, based on the comment about different DDFs in  DCE 7.2.6 and DCE 7.4.0 specifically, do you have both on this same site? If you discover the same device on both, do these values appear differently?

 

As for values not showing up in the web interface specifically, that is not uncommon. Once we verify what we're looking at, we can potentially look into getting an enhancement request into the system should it not already exist and if the issue you're looking to change is getting that value on the web page. I need to know what the device is showing to tell you any more though.


Steve

 

(CID:108827632)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

In response to DCIM_Support
0 Likes
0
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

Hi Garry,

 

Are you able to pull these values from the device directly using SNMP? If the device returns these same values, it would appear that the device or at least the NMC is reading / calculating these values and it's not DCE. If these values are not being shown in the SNMP output of the device then perhaps it is something in DCE. I'm also curious, what firmware is being used on the device(s)? I'm also assuming that bank 6 or at least the outlet that has load on it is 1 hot, neutral, ground and not 2 hots as only 1 phase is showing load.

 

Steve

(CID:108828151)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

In response to DCIM_Support
0 Likes
0
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2024-04-08 10:43 PM

Hi Steve. I only have limited access to the PDU's so cannot use "raw" SNMP to access them. The web interface however reports that Total Power is 0.24KW, Power Factor is 0.76 and Total Apparent Power is 0.31KVA, This equates well to the values above so it suggests to me that this is being reported by the PDU, unaffected by the DDF, and that DCE is receiving a KVA value for Bank 6. Unfortunately the web page does not seem to report the Real or Apparent Power per bank, only the current so I cant confirm if this value is derived from the PDU itself or from the DDF. The PDU is loaded with a single phase load L-N-E so yes 1 hot, neutral and ground. There is one load connected to bank 6 only.

(CID:108828150)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2023-10-22 02:03 AM

0 Likes
0
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:39 AM . Last Modified: ‎2023-10-22 02:03 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of