Emerson/Liebert DSE CRAC - dropping connection in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Emerson/Liebert DSE CRAC - dropping connection in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:04 AM . Last Modified: ‎2024-04-10 01:01 AM

0 Likes
6
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:04 AM . Last Modified: ‎2024-04-10 01:01 AM

Emerson/Liebert DSE CRAC - dropping connection in DCE

Hi. 

I am using DCE 7.2.6 and have 10 Emerson/Liebert DSE CRAC units. All have the same webcard model.

The units run a lead/lag configuration on weekly basis and whenever they switch, DCE looses connectivity to those units even though their webcards remain online and accessible via the browser. 

I have tried rebooting the webcards in the units and then requesting a rescan within DCE with no luck. The only way to get them back 'online' in DCE is to reboot the DCE server itself.  This is not a long-term solution, is there a way to keep the connection between DCE and CRACs or re-establish it automatically?

 

thanks.

(CID:93913911)

Labels
  • Labels:
  • DCIM Support
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

Hi Edward, welcome to the community! We will investigate the issue. It might take more time to reply than usual, because of Christmas holiday. Stay tuned.

(CID:93913995)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

0 Likes
1
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

Hi Edward,

I'm not sure what happens when the devices switch? However it seems like they might be offline/stop reporting for a short while? It is a bit strange they do not reestablish connection once back?

I expect they are reporting using SNMP?

I would recommend trying to maybe increase the timeout value on the devices that are impacted.

Choose the affected device(s) and in the top menu bare choose "Device"->"SNMP Device communication Settings"->"Device Scan Settings"  that will show a menu where timeout and retries can be configured.

(CID:93913997)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

In response to DCIM_Support
0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

Hello,

Are there any other recommendation on this issue.  Our current workaround is to use SNMP1.  This seems to only be an issue when scanning via SNMP3.

(CID:126880223)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

0 Likes
1
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

Hi.

All devices are setup to use SNMP v.3 to communicate with DCE.

There are two different scenarios I am dealing with. Scenario 1: the lead/lag units change their roles. In this case the devices never lose power and the web cards always remain online. 

Scenario 2: during a generator test, all CRAC units temporarily lose power (outage lasts about 1 minute) so the internal web cards go offline until power is restored.

in both scenarios DCE will loose communication with the devices and I have to reboot the DCE server to re-establish connectivity. I took your suggestions and increased the timeout value to the max of 60 seconds (and picked 5 retries).  Will keep monitoring to see if this makes any difference.

One other thing, if any changes are made to the config of the web card inside the CRAC unit, it requires a reboot, and it takes about 4 minutes and 20 seconds for the card to fully re-initialize. I tested the new timeout settings against this reboot on about half the units, and in all cases DCE lost communication to that CRAC. 

(CID:93914109)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

In response to DCIM_Support
0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2024-04-10 01:01 AM

Hi Edward, Thanks for trying this out. Sorry to hear it did not solve the issue. Could you elaborate a bit on how the devices are connected to the DCE? Are they connected to the private LAN? or public LAN? Are they using DHCP/BootP/Static IP? When the DCE server is restarted are the devices connected to DCE using the same IP or are they rediscovered? Scenario 1: How did you verify the device is always online? Did you try to have a ping towards the devices running while they switch roles? Scenario 2: It seems it is not possible to make DCE not detect the webcard "outage". It might be possible to adjust the "communication lost" alarm it self in order not to get this reported. I will need to investigate that.

(CID:93914174)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2023-10-31 10:56 PM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:05 AM . Last Modified: ‎2023-10-31 10:56 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of