Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 01:58 AM . Last Modified: 2022-01-18 02:03 AM
Does NBWL075 have a POE in a Private LAN port?
Can i connect one CameraPod165 directly to Private LAN port of Netbotz 755 Room Monitor?
In a manual for nb750 stated accurately, that 4 Private Lan Ports have PoE,
but in a nb 755 manual there is no such information aboute Private LAN Port:
.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 07:33 AM . Last Modified: 2022-01-18 08:13 AM
Hi @amyshanov ,
Yes, the private LAN port on the 755 is POE.
Initially I thought the unit (itself powered by POE type2) could power 1 camera, I have since found out that if powered properly, it can power both the docked camera as well as one camera connected to the private LAN.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 08:03 AM . Last Modified: 2022-01-18 08:17 AM
You mean, that to connect two cameras to DCE i must build this desigion:
It seem so strange!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 08:10 AM
Hi @amyshanov ,
I re-verified my previous comment (and will correct it. I am now told that if the 755 is powered properly (POE type 2 @ approximately 36w), it can handle the mounted camera and one on the private LAN without additional power.
DCE is secondary in that config.
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.