Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-11 09:16 PM
Hello team,
We have a customer who tried to install trial version of DCE 7.8.1(https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360016284918-DCE-VM-trial-version-download-l... in their VMware ESXi 6.7.
Even though they installed, In webpage, it is showing "Data Center Expert is starting up. Please wait" for a very long time.
Are DCE supposed to deploy only on VMware ESXi 6.5.0.?
Can you suggest ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-22 11:36 AM
Hello @Pothan,
VMWare ESXi 6.5.0 is just what is used by development. I personally would not correlate this issue to an issue with the "supported" ESXI version as the OS is operational and web server is running.
If this is a freshly deployed system, that has only had the apcsetup information setup (network information / username / password), I would suggest a redeployment of the OVA, ensuring to verify the checksum of the OVA file before deployment.
If the issue is still present after that, I suggest reaching out to the local technical support team to have log files gathered and any other necessary steps taken to determine if there is something going on that would not be related to the VMWare ESXi version.
Kind Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-22 11:36 AM
Hello @Pothan,
VMWare ESXi 6.5.0 is just what is used by development. I personally would not correlate this issue to an issue with the "supported" ESXI version as the OS is operational and web server is running.
If this is a freshly deployed system, that has only had the apcsetup information setup (network information / username / password), I would suggest a redeployment of the OVA, ensuring to verify the checksum of the OVA file before deployment.
If the issue is still present after that, I suggest reaching out to the local technical support team to have log files gathered and any other necessary steps taken to determine if there is something going on that would not be related to the VMWare ESXi version.
Kind Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.