Posted: 2021-03-17 01:57 PM
Hi,
How to get exchange rate with web service in DCE?
I want to write the central bank turkey exchange rate in DCE
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-22 11:49 AM
Hi Huseyin,
Here's the DCE web services API section of the help center. If you can't find your answer there, I'd suggest contacting your local technical support for assistance.
https://dcimsupport.ecostruxureit.com/hc/en-us/sections/360006467394-DCE-web-services-API
Best regards,
Jackie
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 12:33 AM
Hi,
this solution for get data from DCE, can you have any example for getting data to DCE
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 05:13 AM
DCE does not support importing data via API, ETL, or any other means. Instead, it can poll devices via snmp or modbus. If you have another device/software that can take in this data point via an API and expose it as an snmp or modbus point, then it can be discovered by DCE and added in.
Alternatively, you could always create a custom property and put in a static value manually which could be used for reports.
Can you elaborate a little more on why you wanted this data point in DCE? I assume it would be related to calculating energy cost?
As an alternative, you could use another dashboarding/reporting tool that can use both DCE's API and this value via an API and combine them that way.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 05:39 AM
Hi Huseyin,
Can I ask for a bigger picture of what you're trying to solve here? Bringing non-sensor data into the DCE is very unusual and not how the platform is designed - perhaps if we better understand the problem, we can better suggest a direction.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 12:32 PM
Hi I tried export data but I get this error in ewsclient but I connected successfully with browser,
Link copied. Please paste this link to share this article on your social media post.