Details of HTTP Post

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Details of HTTP Post
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:21 AM . Last Modified: ‎2024-04-05 03:51 AM

0 Likes
4
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:21 AM . Last Modified: ‎2024-04-05 03:51 AM

Details of HTTP Post

Hello,

My client has SMS server in their system and they want to send SMS DCE alarms to their empoleyees. They want to know the exact data sent via HTTP post. Since I don't have any example, I can not show them any detail about it.

Do you have any example? Can I manipulate the data to reduce it to a SMS message? Do you have any ideas other than HTTP post?

Thanks,

 

(CID:126180724)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:21 AM . Last Modified: ‎2024-04-05 03:51 AM

0 Likes
2
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:21 AM . Last Modified: ‎2024-04-05 03:51 AM

Dear Erhan,

I have tried sending an SMS to the Customer Mobile numbers by using the Customer SMS server by sending Short Message Email(SMS) to the SMS Server Gateway using the following steps. It has worked! Using the Short Message Email, we can limit the characters by specifying the DCE Macros. 

In order to customize email notifications, you would need to use the Short Message Email Option.  Below is a quick how-to guide to create and customiz a new Short Message Email alert. This procedure is useful for those users who want to convert the email alerts into an SMS on their Mobile by using the third party telecom service providers who can convert email alert into an SMS on the target Mobile Numbers.

1) Open the StruxureWare Data Center Expert client.

2) Alarm Configuration Menu > Manage Alarm Actions.

3) Create...

4) Send Short message Email... > Next.

5) Provide an SMS E-mail Action Name and add in the emails that you would like it to go to. 

6) The Subject and message fields can be customized using a defined list of macros that are available:

  • Alert Macros
  • Identification Macros
  • Location Macros

An example of macro usage with their results is listed below.  Text, including spaces within the email will be kept when the information is emailed out.

 

 

Example of sending short message email to SMS server gateway email address & by specifying the intended Mobile numbers in the subject.

 

 

 

After creating a custom Short Message Email, remember to associate it to a Notification Policy. 

 

Alert Macros:

Macro

Example

${ALERTTYPE}

HIGHERR

${SENSORTYPE}

TEMP

${SENSORVAL}

60

${ALERTTIME}

Apr 2, 2009 13:01:45

${ALERTSEV}

ERR, WARN-RTN

${SENSORNAME}

Bldg. 3 Door

${ALERT_PROFILE}

Default, Profile #1

${ALERT_LEVEL}

First Alert Level, Second Alert Level

${ISACTIVE?yes?no}

“active” and “cleared”

${USERURL}

http://www.mysite.com

${USERDESC}

“Too high”

${START_TIME}

13:01:45

${RESOLVE_TIME}

13:07:13

${SENSORLUID}

TEMP1

${SENSORGUID}

B000113_TEMP1

${EVENTID}

3E4512C0FE03440F

${ALERTPOD}

My Pod

${ALERTPODSERIAL}

NB007100730114

${ALERTPORT}

Ext1

${CURRENT_ALERT_NUM}

0, 1, 2

${RESOLVEUSERID}

Joeuser

${RESOLVECOMMENT}

“Turned on the A/C”; “Fixed the leak”

 

 

 

Identification Macros:

Macro

Example

${SERIAL}

5A0902V00025

${IP}

192.168.2.23

${HOSTNAME}

isxc.apc.com

${MODEL}

WallBotz 500

${TIMESTAMP}

998885130

${DATE}

27/03/2009

${YEAR}

2009

${MONTH}

3

${DAY}

27

${TIME}

23-30-01

${HOUR}

23

${MIN}

30

${SEC}

1

${VER}

2_6_2-20071031_1658

 

Location Macros:

Macro

Example

${LOCATION}

Test Lab

${ENCLOSURE}

RACK1234

${SLOT}

A23

${ENCRELLOC}

ATUPS

${ROOM}

C-100

${ROOMROW}

AA

${ROOMCOL}

25

${HEIGHT}

60

${BLDG}

205

${FLOOR}

3

${COMPANY}

APC

${ADDRESS1}

132 Fairgrounds Road

${ADDRESS2}

Building 1

${CITY}

W. Kingston

${STATE}

RI

${COUNTRY}

USA

${CONTACT}

J. Smith

${SITE}

West Campus

${NOTES}

IT Closet, Server Room

${LATITUDE}

30° 18’ N

${LONGITUDE}

97° 42’ W

${GPSLOC}

30° 18’ N / 97° 42’ W

 

I hope this helps. 

Regards,

Bala

 

(CID:126180788)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:21 AM . Last Modified: ‎2024-04-05 03:51 AM

0 Likes
2
2174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:21 AM . Last Modified: ‎2024-04-05 03:51 AM

Dear Erhan,

I have tried sending an SMS to the Customer Mobile numbers by using the Customer SMS server by sending Short Message Email(SMS) to the SMS Server Gateway using the following steps. It has worked! Using the Short Message Email, we can limit the characters by specifying the DCE Macros. 

In order to customize email notifications, you would need to use the Short Message Email Option.  Below is a quick how-to guide to create and customiz a new Short Message Email alert. This procedure is useful for those users who want to convert the email alerts into an SMS on their Mobile by using the third party telecom service providers who can convert email alert into an SMS on the target Mobile Numbers.

1) Open the StruxureWare Data Center Expert client.

2) Alarm Configuration Menu > Manage Alarm Actions.

3) Create...

4) Send Short message Email... > Next.

5) Provide an SMS E-mail Action Name and add in the emails that you would like it to go to. 

6) The Subject and message fields can be customized using a defined list of macros that are available:

  • Alert Macros
  • Identification Macros
  • Location Macros

An example of macro usage with their results is listed below.  Text, including spaces within the email will be kept when the information is emailed out.

 

 

Example of sending short message email to SMS server gateway email address & by specifying the intended Mobile numbers in the subject.

 

 

 

After creating a custom Short Message Email, remember to associate it to a Notification Policy. 

 

Alert Macros:

Macro

Example

${ALERTTYPE}

HIGHERR

${SENSORTYPE}

TEMP

${SENSORVAL}

60

${ALERTTIME}

Apr 2, 2009 13:01:45

${ALERTSEV}

ERR, WARN-RTN

${SENSORNAME}

Bldg. 3 Door

${ALERT_PROFILE}

Default, Profile #1

${ALERT_LEVEL}

First Alert Level, Second Alert Level

${ISACTIVE?yes?no}

“active” and “cleared”

${USERURL}

http://www.mysite.com

${USERDESC}

“Too high”

${START_TIME}

13:01:45

${RESOLVE_TIME}

13:07:13

${SENSORLUID}

TEMP1

${SENSORGUID}

B000113_TEMP1

${EVENTID}

3E4512C0FE03440F

${ALERTPOD}

My Pod

${ALERTPODSERIAL}

NB007100730114

${ALERTPORT}

Ext1

${CURRENT_ALERT_NUM}

0, 1, 2

${RESOLVEUSERID}

Joeuser

${RESOLVECOMMENT}

“Turned on the A/C”; “Fixed the leak”

 

 

 

Identification Macros:

Macro

Example

${SERIAL}

5A0902V00025

${IP}

192.168.2.23

${HOSTNAME}

isxc.apc.com

${MODEL}

WallBotz 500

${TIMESTAMP}

998885130

${DATE}

27/03/2009

${YEAR}

2009

${MONTH}

3

${DAY}

27

${TIME}

23-30-01

${HOUR}

23

${MIN}

30

${SEC}

1

${VER}

2_6_2-20071031_1658

 

Location Macros:

Macro

Example

${LOCATION}

Test Lab

${ENCLOSURE}

RACK1234

${SLOT}

A23

${ENCRELLOC}

ATUPS

${ROOM}

C-100

${ROOMROW}

AA

${ROOMCOL}

25

${HEIGHT}

60

${BLDG}

205

${FLOOR}

3

${COMPANY}

APC

${ADDRESS1}

132 Fairgrounds Road

${ADDRESS2}

Building 1

${CITY}

W. Kingston

${STATE}

RI

${COUNTRY}

USA

${CONTACT}

J. Smith

${SITE}

West Campus

${NOTES}

IT Closet, Server Room

${LATITUDE}

30° 18’ N

${LONGITUDE}

97° 42’ W

${GPSLOC}

30° 18’ N / 97° 42’ W

 

I hope this helps. 

Regards,

Bala

 

(CID:126180788)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:22 AM . Last Modified: ‎2024-04-05 03:51 AM

In response to DCIM_Support
0 Likes
0
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:22 AM . Last Modified: ‎2024-04-05 03:51 AM

Hi Erhan,

 

I would definitely suggest following Bala's example. If you're not already familiar with HTTP posts, it is likely not something you want to get into. An HTTP post sends an XML file to an HTTP server that is specific designed to sit and listen for such posts then parse the data it receives. 

 

Steve.

(CID:126181127)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:22 AM . Last Modified: ‎2024-04-05 03:51 AM

In response to DCIM_Support
0 Likes
0
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:22 AM . Last Modified: ‎2024-04-05 03:51 AM

Thanks for fast and fully explained response Balaraman. I will try that option. 

Thank you Steve. At least, now I know what HTTP post like.

Best regards,

(CID:126183867)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:22 AM . Last Modified: ‎2023-10-22 01:52 AM

0 Likes
0
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:22 AM . Last Modified: ‎2023-10-22 01:52 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore