Denco CRAC not showing all sensor values in DCO

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Denco CRAC not showing all sensor values in DCO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

0 Likes
6
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

Denco CRAC not showing all sensor values in DCO

Hi,

For an ongoing project, I had uploaded new DDF for DENCO unit DMA065 and I am getting correct values in DCE 7.4.1 and its perfect.

But in DCO 8.0.3 I am only seeing Humidity values for the CRAC as below.

Need to have all temperature values to associate on to the layout.

Please someone suggest how can we have full sensor values in DCO for a Mutivendor CRAC?

Thanks & Regards

Shemil

 

 

(CID:116361498)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

Hi shemilusman,

I can't claim, but it is perhaps necessary to try this New Features in StruxureWare Data Center Operation 8.1.

With best regards.

(CID:116361558)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

0 Likes
3
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

Hey @shemilusman,

This looks like an issue with the DCO support, to give DCO support we create a patch file which is not provided to the customer unless he specifies that he needs DCO support. This patch file when applied in DCE might fix the issue you're facing.

The XML patch file is uploaded in a box folder with link - https://schneider-electric.box.com/s/tocjoz85lx5r2w4rz7qslfvysnxxappz 

Please follow the instructions given below to get everything in place. 

How do I apply the patch in DCE? 
1. Make sure to have a recent backup in place of your running systems before applying the patch. 
2. On the DCE server, open this URL: http:///nbc/status/SensorContexts (replace with your server IP) can be also done through a browser with in DCE servers network. You must be logged in as an admin user.
3. Upload the patch file (cooling_device.xml) given. The file has now been uploaded to the server and the patch is in place.

Please let us know if this worked for you or if you have any issues in accessing the box folder link.

Regards,

Moloy Das

(CID:116361687)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

In response to DCIM_Support
0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

Hi Moloy Das,

And it will also be required to apply this patch to future versions of DCO, for example DCO-8.1, or not?

Very thanks for the support.

(CID:116361699)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

In response to DCIM_Support
0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

I already independently understood: above the stated patch file needs to be applied irrespective of the version of the DCO and DCE servers.

Very thanks for the support.

(CID:116361716)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

In response to DCIM_Support
0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2024-04-08 01:15 AM

Glad I could help.

(CID:116361770)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2023-10-22 01:52 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:37 PM . Last Modified: ‎2023-10-22 01:52 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore