EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:00 PM . Last Modified: 2024-04-04 11:43 PM
Hi Im running DCO 8.2.2 with capacity licence, I have two DC's at different locations and I have ac units and ups's associated to the relevant physical device but I'm finding issues. In the web portal only one location is showing power and 'u'space location 1 is correct however location 2 also has 10 + racks and 2 x 180 kW UPS.
In the DCO client no measured values are displayed at all power or cooling
TIA
Mike
(CID:131963918)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:00 PM . Last Modified: 2024-04-04 11:43 PM
Was location 2 created recently?
Capacity calculation is done daily at specific time, you can check this under Client preference.
If yes, by the time you read this, you should see the capacity info updated ...
(CID:131964108)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:00 PM . Last Modified: 2023-10-22 01:45 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.