Posted: 2020-07-05 05:00 PM
This question was originally posted on DCIM Support by Alessio De Maio on 2019-02-11
Hello,
I have an Oracle rack PDU that is displaying a bunh of sensors data on DCE, but when I associate to a rack PDU in DCO it doesn't display any measured sensor.
The Oracle Rack PDU is a RMII_PDU15KVA-3_HV, there isn't a DDF for DCE here on the DDF section, so I created my own, and it's working the way I needed it on DCE.
Here some screenshot:
Thank you for your help.
(CID:139694208)
Posted: 2020-07-05 05:00 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2019-02-11
Hi Alessio,
It appears to be DDF related issue. It seems DCO is not receiving the expected sensor data, for detail description please see the following page:
https://sxwhelpcenter.ecostruxureit.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO
New DDF(s) can be requested at Device support site: https://ddf.ecostruxureit.com/
Kind regards
(CID:139694228)
Posted: 2020-07-05 05:00 PM
This comment was originally posted on DCIM Support by BURHAN TOPAL on 2019-03-22
Could you send an email the DDF file its your created? burhantopal@gmail.com
(CID:141266254)