DCO lost connection with DCE on upgrade to 7.2.7

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO lost connection with DCE on upgrade to 7.2.7
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

0 Likes
7
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

DCO lost connection with DCE on upgrade to 7.2.7

Hi I have recently upgraded a clients site DCE to 7.2.7 no problems. However when the client has tried to launch DCO it fails, as DCE is configured to act as authentication server the following message pops up

Unable to validate your user credentials 

It appears the connection between the 2 has vanished within DCO but the client in his wisdom has locked down the only local user account to viewer only so cant even establish or test the link can someone please help!!

Oh forgot to mention:

OPS is on version 7.3.6 i know i need to upgrade it but this shouldn't cause this issue

(CID:103585795)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

0 Likes
2
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Mike,

 

Sorry, did not realize but that was a Schneider only post. Basically one of our field service personnel had a similar issue where DCO was using DCE for authentication. The DCE server had just had it's SSL cert replaced so the DCO server now needs to update it's cert to be able to authenticate.

In this case as well, the local user needs to be able to log in so that the cert can be updated. Even if this is not the case, the local user will be required to gain access if remote users can not be authenticated for whatever reason.

 

Steve.

(CID:103585812)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

0 Likes
2
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Mike,

 

They will need to log in to DCO using the local user. They may have to work with tech support if they have somehow disabled that user. As for what may have happened, was DCO using SSL to connect to DCE? Installing DCE could have simply created a new SSL cert that requires confirmation do download so they can connect. I'm thinking you're maybe seeing something similar to this post.

 

Steve

(CID:103585805)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

In response to DCIM_Support
0 Likes
0
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Steve this link is asking for a Schneider email address login could you please copy and paste? Cheers Mike

(CID:103585809)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

In response to DCIM_Support
0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:43 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Mike, Please check your email - I've send you instructions to create a recoveryuser, thanks.

(CID:104173875)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

0 Likes
2
703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Mike,

 

Sorry, did not realize but that was a Schneider only post. Basically one of our field service personnel had a similar issue where DCO was using DCE for authentication. The DCE server had just had it's SSL cert replaced so the DCO server now needs to update it's cert to be able to authenticate.

In this case as well, the local user needs to be able to log in so that the cert can be updated. Even if this is not the case, the local user will be required to gain access if remote users can not be authenticated for whatever reason.

 

Steve.

(CID:103585812)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

In response to DCIM_Support
0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Steve the client has disabled the local access user and allowed viewer only is there a way i can gain access via the back door (as such) and insert a new local user with full admin rights?? I have spoke with the client and raised the point that if the connection between the 2 devices was to fail you will be locked out as such is the case.

 

Cheers,

 

Mike

(CID:103586397)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

In response to DCIM_Support
0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2024-04-09 02:42 AM

Hi Mike,

 

You need to contact local support. The user needs to be re-enabled and I can not do it via this forum. Support in your region will have to assist you, sorry.

 

Steve

(CID:103586398)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2023-10-31 10:50 PM

0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:44 PM . Last Modified: ‎2023-10-31 10:50 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of