Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:47 PM . Last Modified: 2024-04-05 02:31 AM
Blades without family (empty Product family field) located in a blade enclosure also without family ...

... can be moved into a blade enclosure, that has a Product family:

For some reason, this action is not allowed in the web client:

Sorry for the sad story about missing families, but this limitation is impacting a customer who uses the web client for decommissioning blades into enclosures.
Unfortunately, it is not possible to change (or clear) the product family on-the-go:
(CID:129403270)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:47 PM . Last Modified: 2024-04-05 02:31 AM
Hi Christian,
Changes has been made to DCO in order to solve above mentioned behaviour and align functionality between desktop and web client. The changes are available in the latest release (8.2.12)
It is now allowed both in web and desktop client to add/move a blade if:
Blade Enclosure has a family, blade must be of same family or no family.
Blade Enclosure has no family, blades of any family or no family is allowed.
Hopefully this explains the new functionality.
Furthermore I believe we have fixed the specific customer case offline.
/Søren
(CID:137727305)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:47 PM . Last Modified: 2024-04-05 02:31 AM
Hi Christian,
Many thanks for the nice description - can be reproduce. I have registered an enhancement case for this, so the codes could be reviewed, thanks.
Kind regards
(CID:129404008)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:47 PM . Last Modified: 2024-04-05 02:31 AM
Hi Christian,
Changes has been made to DCO in order to solve above mentioned behaviour and align functionality between desktop and web client. The changes are available in the latest release (8.2.12)
It is now allowed both in web and desktop client to add/move a blade if:
Blade Enclosure has a family, blade must be of same family or no family.
Blade Enclosure has no family, blades of any family or no family is allowed.
Hopefully this explains the new functionality.
Furthermore I believe we have fixed the specific customer case offline.
/Søren
(CID:137727305)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:48 PM . Last Modified: 2023-10-22 01:42 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.