Just for clarity please....
in DCO how would you set them up in this scenario?
1x UPS with N+1 redundancy with 2 feeds to PDPM277H style distribution boards with each one feeding an A and B rPDU in the racks. Assume all servers have dual power supplies with 1 feed from rPDU A and 1 feed from rPDU B.
What should the server power settings be setup as?
I await your answers...
Regards
(CID:133369901)
Posted: 2020-07-04 09:33 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-15
Hi Garry,
For this setup (nice illustration) I would use "Distribution Redundancy N+1" settings for server. As described in the following page: What does the power tool tip tell me, this is a combination of "Distribution Redundancy" and "N+1". For this type of redundancy, the power distribution is redundant and there is internal redundancy on the UPS level (one UPS with one redundant power module).
Kind regards
(CID:133371491)
Posted: 2020-07-04 09:33 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-15
Hi Garry,
For this setup (nice illustration) I would use "Distribution Redundancy N+1" settings for server. As described in the following page: What does the power tool tip tell me, this is a combination of "Distribution Redundancy" and "N+1". For this type of redundancy, the power distribution is redundant and there is internal redundancy on the UPS level (one UPS with one redundant power module).
Kind regards
(CID:133371491)
Posted: 2020-07-04 09:34 PM
This comment was originally posted on DCIM Support by Garry Priestland on 2018-08-17
Thanks Jef. I had been previously advised that this would be N+1 because the UPS is N+1. Can't remember the source of this as it was so long ago...
After setting the servers up this way I noted that DCO will not calculate potential failover load so changed some of them to "Distribution Redundancy N+1" and the figures seemed to make more sense.
I am even happier that I was right in what I thought...
Thanks again