Posted: 2020-07-03 11:24 PM
This question was originally posted on DCIM Support by Andrew Trabert on 2017-09-15
I have a project coming up and need to model a 8kva single phase UPS' and power path. I know I need to use floor mount units, however when I tried to use a 2 pole 208 breaker on the PDU, it doesn't show up, only the single pole breaker does. I did set the pdu output voltage to 208/60.
The only work around seems to be to use a 3ph UPS & PDU and only use 2 phases.
Does anyone else have any other suggestions?
(CID:124528340)
Posted: 2020-07-03 11:24 PM
This answer was originally posted on DCIM Support by Gert Lehmann on 2017-09-26
In the genomes you can create a single pole breaker with the size of 2 (just copy the exiting 1P breaker) and use that, it will then look like (and occupy the same space as) a 2 pole breaker.
Since DCO does not consider the pole count for single phase UPS's, this solution will work just similar to having an actual 2 pole breaker.
I would not recommend using a 3 phase UPS, because it is always going to result in having non-utilized capacity on the power phase not used, which means the capacity calculations are going to be wrong.
The only case where using a single phase UPS would not work, is if the actual UPS is a split-phase-UPS, e.g. it has 2 phases + neutral as output, because it would then both have 120V and 208V outputs which you cannot do with a single phase UPS in DCO.
Regards
Gert
(CID:125212114)
Posted: 2020-07-03 11:24 PM
This comment was originally posted on DCIM Support by Ditte Drewer Mathiasen on 2017-09-18
Hi Andrew Trabert, thanks for posting.
Let's hope you find your answer here.
Kind regards Ditte
(CID:125208495)
Posted: 2020-07-03 11:24 PM
This answer was originally posted on DCIM Support by Gert Lehmann on 2017-09-26
In the genomes you can create a single pole breaker with the size of 2 (just copy the exiting 1P breaker) and use that, it will then look like (and occupy the same space as) a 2 pole breaker.
Since DCO does not consider the pole count for single phase UPS's, this solution will work just similar to having an actual 2 pole breaker.
I would not recommend using a 3 phase UPS, because it is always going to result in having non-utilized capacity on the power phase not used, which means the capacity calculations are going to be wrong.
The only case where using a single phase UPS would not work, is if the actual UPS is a split-phase-UPS, e.g. it has 2 phases + neutral as output, because it would then both have 120V and 208V outputs which you cannot do with a single phase UPS in DCO.
Regards
Gert
(CID:125212114)
Posted: 2020-07-03 11:24 PM
This comment was originally posted on DCIM Support by Andrew Trabert on 2017-09-26
Thank you! That solution will work since these are not split phase ups', and as far as I know, they do not have a step down transformer (however I guess that could be modeled as a separate pdu).
Is it currently on the roadmap/or is there an enhancement request to add 120/208 output from a single phase UPS'?
(CID:125212323)