Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:09 PM . Last Modified: 2024-04-09 02:54 AM
All,
customer does have DCE 7.2.7 & DCO 7.5, DCE is monitoring MGE Galaxy 5000 UPS, this UPS is associated with the UPS in the DCO model, this was done more then a week ago but still no measured data is shown in DCO, attached is the DDF version of the MGE UPS within DCE, devices sensor's of the UPS and the UPS within DCO, what can be the cause of this, is it the DDF file ?
(CID:103584571)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:09 PM . Last Modified: 2024-04-09 02:54 AM
Hi Cees,
Many thanks for sharing the device sensors - it seems as you've mentioned, it is ddf related issue and you need to get customized/new DDF file(s) from the multivendor support team ( multivendorsupport@apcc.com).
The DDF file(s) expected to contain the following sensor Type:
Power Sensors:
OUTPUT_POWER_WATTS
OUTPUT_POWER_TOTAL_WATTS
MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER
Amp Sensors:
MODULE_BREAKER_CURRENT
OUTPUT_CURRENT
OUTPUT_CURRENT_TOTAL
INPUT_CURRENT
More details available here:
http://dcimsupport.apc.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO
Kind regards
(CID:103584592)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:09 PM . Last Modified: 2024-04-09 02:54 AM
Hi Cees,
Many thanks for sharing the device sensors - it seems as you've mentioned, it is ddf related issue and you need to get customized/new DDF file(s) from the multivendor support team ( multivendorsupport@apcc.com).
The DDF file(s) expected to contain the following sensor Type:
Power Sensors:
OUTPUT_POWER_WATTS
OUTPUT_POWER_TOTAL_WATTS
MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER
Amp Sensors:
MODULE_BREAKER_CURRENT
OUTPUT_CURRENT
OUTPUT_CURRENT_TOTAL
INPUT_CURRENT
More details available here:
http://dcimsupport.apc.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO
Kind regards
(CID:103584592)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:09 PM . Last Modified: 2023-10-31 10:47 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of