Hi All ,
I just monitor 12 Temp sensor via netbotz200 and associate to DCO 7.5 , when I turn into 3D mode ,
there are some space on the screen ,pls see the photo as attachment , My concern is why it still appear this
issue on DCO 7.5 ? Any solution for it ? Many thanks .


Best Regards
(CID:105468887)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:13 AM . Last Modified: 2024-04-09 12:40 AM
Hi Chu Li,
It might be, basically the application doesn't have enough temperature information to cover the whole area, as a quick test I would add some temperature sensors to those "empty" area and see if there any changes. If it doesn't, would it be possible to share a copy of the latest backup file with me, thanks.
Kind regards
(CID:105468935)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:13 AM . Last Modified: 2024-04-09 12:40 AM
Hi Chu Li,
Many thanks for sharing the copy of your backup file with me - based on the available temperature information and the location of the equipment, it seems the 3D simulation is unable to cover the temperature map for whole area.
As a simple test, I tried adding/associating a temperature sensor to one of the cooling units (I-14), and the tried the simulation:
Or perhaps, as a work around, it might be considered to move the cooling unit I-14 closer to it's neighbor:
Hope this helps,
Kind regards
(CID:105469192)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:13 AM . Last Modified: 2023-10-31 10:46 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.