DCE7.5 + DCO8.2 Monitoring Error

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE7.5 + DCO8.2 Monitoring Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:21 PM . Last Modified: ‎2024-04-04 04:13 AM

0 Likes
6
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:21 PM . Last Modified: ‎2024-04-04 04:13 AM

DCE7.5 + DCO8.2 Monitoring Error

Hello community.

My customer has two datacenters, in each one they have:

  1. DCE (7.4.3) Upgraded to 7.5
  2. DCO (8.0) Upgraded to 8.2
  3. Portal
  4. DCO - Disaster Recovery

Before upgrade DCE 7.4.3 monitored the DCO without errors, the database status reported by DCE was normal, but now, after the upgrade of both systems (DCE and DCO + DCO-DR) the reported status:

a. The StruxureWare Operations database status is unknown

b. The Struxureware Operations Server is unreachable

In first time I think maybe a customer´s network issue could be the cause, but after check the network health and some tests I tried installing a DCE demo in version 7.5 and DCO demo in version 8.2 in my laptop using vmware player and I get the same error messages....

Community, do you have any idea about the possible reasons? Could DCO 8.2.7 be a cure for this situation? for your time and support thank you very much.

Best Regards, 

 

(CID:132666514)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:21 PM . Last Modified: ‎2024-04-04 04:13 AM

0 Likes
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:21 PM . Last Modified: ‎2024-04-04 04:13 AM

Hi, 

I had the same issue. It was solved with update of DCO to v 8.2.7

(CID:132666574)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

0 Likes
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

Dear Erlinson Bravo Garcia,

Boris Majdandzic is right, this is a very known bug that, according to Jef Faridi answer in topic :

Update:


DCO 8.2.7 is released now, contains the fix.

With respect.

(CID:132666605)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

0 Likes
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

Hello Community, 

I think it´s on the dco side, I ran the isx_devicewalk and I get OID answers, when I compare with the schneiderops.xml file I can see that dce show the readed status of the respective OID example:

In dce one error alarm is: Unknown status for ETL (in red color, severity:Error)

In schneiderops.xml I think the OiD is :

-

state

OPS_ETL_STATUS


-


-

.1.3.6.1.4.1.318.1.2.2.1.5.0

etl_status_enummap

and the result for this oid (1.3.6.1.4.1.318.1.2.2.1.5.0) in the walkfile is :

1.3.6.1.4.1.318.1.2.2.1.5.0   , Integer     , 1

In the xml file the status codes for this OiD are:

-








I Think dce is reading this value and reporting the status for that, I verified the communities (public/private) all are for defect config, I don´t have firewall rules in my virtual machines ...

 

Any idea about this situation? 

 

Thank you very much.

(CID:132666607)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

Ok spezialist I´m just trying to download the 8.2.7 and comment soon...

Thank you.

 

(CID:132666613)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2024-04-04 04:13 AM

Dear Erlinson Bravo Garcia,

Tell us, please, did you solve your problem or not?

With respect.

(CID:132670092)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2023-10-22 01:29 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:22 PM . Last Modified: ‎2023-10-22 01:29 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore