DCE v7.5.0 Application Bug/Java Exception

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE v7.5.0 Application Bug/Java Exception
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:07 AM . Last Modified: ‎2024-04-04 01:11 AM

0 Likes
20
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:07 AM . Last Modified: ‎2024-04-04 01:11 AM

DCE v7.5.0 Application Bug/Java Exception

Hi all,

We have a DCE system (v.7.5.0) with the following problem:

 

1.- When doing a double click on an active alarm to see its detail , the application throws this error (see the screen)

 

2.- We reboot the virtual machine to see if it corrects and the DCE stays in an infinite boot loop (see the screen)

 

At the moment we are waiting for a backup of the VM to be restored, to put the system back into production

Has it ever happened, something similar?

Thanks,

(CID:134036496)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 20
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

0 Likes
3
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

Hi Ivan,

 

I can't say that this is anything that I've seen before.  Just by the fact that you rebooted and the server didn't appear to fully reboot points to a server side issue but without more detail I can't say what causes the client message or if it would be the same as the server log. It is quite likely that after some brief troubleshooting, tech support would have suggested a similar approach by re-deploying and importing a backup.

If the issue returns however, this may be something a little more in-depth than is usually handled for DCE on this forum and you, or more specifically your customer, might want to contact tech support directly while experiencing the issue so they can gather detail, logs, etc. in a more timely manner.

 

Steve

(CID:134036655)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

In response to DCIM_Support
0 Likes
0
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

Hi Steve,

 

Is there any way to access the server log, when it is in this state?

(CID:134036681)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

In response to DCIM_Support
0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

Hi Ivan,

 

The web page appeared to not have the link so you can try:

http://dcecruz.bjumper.com/capturelogs. Delete any existing logs and create a new archive. There is not much here that is user friendly and I'd still suggest working with support on this.

Other than that, the only way to obtain the logs would be with root access. We do not provide this to customers so again, it would require direct tech support contact. They may be able to (with the customer's permission) remotely access the server and get in to access the logs. 

 

Steve

(CID:134036691)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

In response to DCIM_Support
0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

Hi Steve,

It does not let me access the logs (see the screen)

 

I have opened a case in support this morning, I am waiting for an answer. 

Any more ideas?

Thank you anyway

 

 

(CID:134036703)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-05-09 03:58 AM

0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-05-09 03:58 AM

Dear igonzalez,

With the above Java error in the DCE-client, I have not yet encountered.

Can you clarify after what changes/events occurred the above error? How long did the DCE-server work without rebooting?

In any case, I'm curious to know if you can restore the DCE-server from a backup.

With respect.

(CID:134036657)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

Hi, 

The error occurred when seeing the detail of an alarm that did not return to its normal value after the threshold fell. (There were no previous configuration changes)

The server was operational after the error and manually restarted.

From here the server died.

I am crossing the fingers so that the restoration of the VM backup works and starts normally.

 

(CID:134036678)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

0 Likes
1
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 01:11 AM

Hi all,

Here attach the DCE Client Log, In case it throws some light

Thanks,

DCE Client log.zip

(CID:134036715)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:08 AM . Last Modified: ‎2024-04-04 12:59 AM

Hi Ivan,

 

There really isn't anything I can tell from these client logs, simply looks like it can't pull the proper data from the server. Since the server is having issues and can't boot, that would seem logical anyway. It's a server side issue and your local support team will have to help you with the logs.

Steve

(CID:134036847)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

0 Likes
10
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Hi all,

I just had the bad news.

The existing VM level backup (15d retention) has the same problem after its restore.

the problem has been hidden for a long time, and until the server was restarted, it was not known.

I hope support answer, but any idea arrived at this point will be welcome.

Thanks,

(CID:134036827)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Dear Iván González Borraz,

Please, open the VMware console of the DCE virtual machine and restart it. Look carefully at the process of booting the DCE-server, what are there visible problems? What messages/errors stops the process of booting a DCE-server?

From your comments:

The existing VM level backup (15d retention) has the same problem after its restore.

Do you mean backup using native VMware vSphere tools or native DCE-server backup?

Try create a clean virtual machine DCE-7.5.0 from the provided SE ova-file (the MAC address must be the same). And then deploy a full backup (native DCE-server full backup) to this virtual machine. Then it will be possible to see if the above problem will again appear or not?

With respect.

Then create a clean virtual machine DCE-7.5.0 from the provided SE ova-file (the MAC address must be the same). And then deploy a full backup to this virtual machine. Then it will be possible to see if the above problem will again appear or not?

(CID:134036862)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Hello,

I attach the screenshots of the console during startup

see something?

The existing Backup is from the VMware backup tool. (full VM) There is no backup of files at the DCE level.

Thanks,

 

(CID:134037555)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Dear Iván González Borraz,

From your comment:

...The existing Backup is from the VMware backup tool. (full VM) There is no backup of files at the DCE level.

This is very very bad. You probably already are convinced this...

Your first screenshot is a screenshot of the start the booting of the DCE-server. But your second screenshot is a screenshot of the completion the process of restarting the DCE-server (it shows that the system processes STOP).

Can you confirm that the process of booting the DCE-server ends normally? After the successful booting of the DCE-server, what is displayed on the console?

With respect.

(CID:134037637)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Hi,


If I know it is very bad...

The boot process finishes and gives me pront to system login (apc info) attached screen

 

The DCE client says it is booting.

The DCE Wed client stays in an infinite loop with this screen

 

(CID:134037661)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Dear Iván González Borraz,

Tell us, please, did you solve your problem or not?

Recently, a new version of DCE-7.6.0 has been released: 

With respect.

(CID:134679951)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Thanks for the information, but it is not resolved yet.


I'm waiting for support response

(CID:134680247)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:09 AM . Last Modified: ‎2024-04-04 12:59 AM

Ok, if there is news on your support case (you opened it by contacting =SE= local techsupport?), it will be interesting to me.

With respect.

(CID:134680251)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2024-04-04 12:59 AM

Hi,

I opened it via web

incident in the Schneider system (N.52382872) (ref: _00DA0abSm._5001Hqm6Z8: ref) 


Thanks,

(CID:134680253)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2024-04-04 12:59 AM

Hi Ivan,

i saw that you had opened an email ticket and we’ve requested that local support get back to you. Just an FYI, a phone call to support is usually much quicker. 

 

Steve. 

(CID:134680533)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2024-04-04 12:59 AM

In response to DCIM_Support
0 Likes
0
3400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2024-04-04 12:59 AM

Thanks Steve, 

 

They contacted me last week, they are analyzing information that I sent them.

(CID:134680591)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2023-10-22 01:28 AM

0 Likes
0
3399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 12:10 AM . Last Modified: ‎2023-10-22 01:28 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore