Good Day,
i have never done this type of connection so please excuse me if i sound stupid, how can i connect a power logic PM700 to DCE? Can i use an RS485 to Ethernet converter? or is there a better or simpler way?
(CID:140713445)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:57 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-13
Hi Terrence,
I believe your first instinct is correct. Assuming the meter only has 232 or 485 and no Modbus over tcp, you’ll need a Modbus serial to ip gateway. I believe the current one we suggest is the EGX150. You’ll then also need to hit the DDF link on the top of the page and request the proper DDF.
Thanks,
Steve.
(CID:140713466)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:57 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-13
Hi Terrence,
I believe your first instinct is correct. Assuming the meter only has 232 or 485 and no Modbus over tcp, you’ll need a Modbus serial to ip gateway. I believe the current one we suggest is the EGX150. You’ll then also need to hit the DDF link on the top of the page and request the proper DDF.
Thanks,
Steve.
(CID:140713466)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:57 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.