Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84766members
354199posts

DCE power logic

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
DCIM_Support
Picard
Picard
0 Likes
2
252

DCE power logic

This question was originally posted on DCIM Support by terrence ramnarine on 2019-03-13


Good Day, 

i have never done this type of connection so please excuse me if i sound stupid, how can i connect a power logic PM700 to DCE? Can i use an RS485 to Ethernet converter? or is there a better or simpler way?

(CID:140713445)


Accepted Solutions
DCIM_Support
Picard
Picard
0 Likes
0
252

Re: DCE power logic

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-13


Hi Terrence,

I believe your first instinct is correct. Assuming the meter only has 232 or 485 and no Modbus over tcp, you’ll need a Modbus serial to ip gateway. I believe the current one we suggest is the EGX150. You’ll then also need to hit the DDF link on the top of the page and request the proper DDF.

 

Thanks,

Steve. 

(CID:140713466)

See Answer In Context

2 Replies 2
DCIM_Support
Picard
Picard
0 Likes
0
253

Re: DCE power logic

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-13


Hi Terrence,

I believe your first instinct is correct. Assuming the meter only has 232 or 485 and no Modbus over tcp, you’ll need a Modbus serial to ip gateway. I believe the current one we suggest is the EGX150. You’ll then also need to hit the DDF link on the top of the page and request the proper DDF.

 

Thanks,

Steve. 

(CID:140713466)