DCE monitors DCO PUE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE monitors DCO PUE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
49
2947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

DCE monitors DCO PUE

If you have DCO and want the PUE dashboard amount shown by your SNMP monitor, especially DCE, here is a way to do it.

DCO PUE in DCE V2.pdf

Cheers,

Ed

(CID:136153387)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 49
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

Dear Stine Hansen,

Tell me please, the attachment below is not available only for my EcoStruxure IT user account or for all EcoStruxure IT users (non-employees =SE=)? If so, why?

Very thanks for the support.

(CID:136644429)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

Is your browser removing the link? I can see and download the pdf attached on this page.

Regards

Greg Sterling

(CID:136644498)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

Dear Greg Sterling,

No, it does not depend on the browser or on the PC, etc. It looks like this is a feature from =SE= for me ☹️...

Very thanks for the support.

(CID:136644504)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:15 PM . Last Modified: ‎2024-04-03 11:59 PM

same issue to me

 

(CID:136644526)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

Hi spezialist, to avoid disclosure of sensitive information in attachments we have chosen to limit the visibility of certain attachments.

Thanks,

Stine 

(CID:136644583)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

If it's not public, why Ed Tarento has publised here?

 

(CID:136644594)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

It's not Ed who has hidden the attachment. It's our policy to hide certain attachments. We're currently working on identifying and releasing attachments that don't reveal any sensitive information.

Thanks,

Stine

(CID:136644610)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

Dear Stine Hansen,

Thanks for the support: now I can see the pdf document in this topic well and can download it 😀.

With respect.

(CID:136644783)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:59 PM

thanks Stine and ed. 

(CID:136645290)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

I tried editing my original post but some errors so here's V2 instructions, adding some trouble shooting info and some minor changes.  Let me know how you go

DCO PUE in DCE V2.pdf

Cheers

Ed

(CID:137733103)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

Dear Stine Hansen,

Could you again help fix the inaccessibility of the file V2 instructions published by Ed Tarento?

Very thanks for the support.

(CID:137733204)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

DCO PUE in DCE V2.pdf

(CID:137733520)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:16 PM . Last Modified: ‎2024-04-03 11:58 PM

Try that

(CID:137733522)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Unfortunately the result is the same:

With respect.

(CID:137733538)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi spezialist and Ed Tarento,

there seems to be a bug here. We're working on it.

Thanks,

Stine

(CID:137733558)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Hello,

At the time being we don't have a way to mark individual attachments as safe, thus we do it explicitly. A new upload will take a new ID and we will have to approve and whitelist it again, manually.

We will be working on making something more robust for future.

(CID:137733611)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

thanks Ed

(CID:138380976)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

This is fantastic, thanks for sharing. Everything was working fine but now when i look at the PUE sensor it's saying  "Offline" and I'm not getting any data. 

(CID:141268047)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi Andrew

Thanks for the feedback.  Does the DCO PUE Dashboard work?  show a figure you're expecting?  Is DCE properly reporting the status of the DCO server?  If needed, please also check "Troubleshooting" in the attached DCO PUE in DCE V2.pdf

Let us know how you go

Cheers

Ed

(CID:141268049)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

PUE is working on DCO and DCE has values from yesterday, it appears to stop working at midnight. snmp.conf is correct and getPUE is a copy of the txt in the file so that should be correct. 

If i run the test script i get the result 

(23) Failed writing body
./test.sh: line 8: /1/ {print $2}: No such file or directory

 

ls dir is

-rwxr-xr-x.  1 root root   900 Mar 28 09:28 getPUE.sh

 

 

(CID:141268065)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Andrew, 

Check the line in test.sh is a single line

pue=`/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '/1/ {print $2}'|awk -F"," '/1/ {print $1}' `

and not 2 lines as it show in the PDF

I'll update the doco to make this clear

Let me know how you go

Ed

(CID:141268097)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Perfect, test script works and returns the correct value. What's also interesting is that at midnight last night we started receiving data again. 

Am i correct in assuming that  DCO only calculates the PuE once a day, the values for PuE are the same for the 24h period, or is this an issue with the way that I have this setup? 

Thanks for the assistance 

(CID:141268615)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:17 PM . Last Modified: ‎2024-04-03 11:58 PM

Glad its working.  I know that the value only changes once per day and I assume its therefore only calculated once per day.

Cheers

Ed

(CID:141268623)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi Ed Tarento,

Glad to be able to search your valuable input here.

Is this method calculating historical PUE from DCE and DCO still applicable the latest DCE and DCO version?

 

Thanks,

Fergus

(CID:146670089)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi Fergus.  I'm not aware of any reason this solution should not still work.  Have you tried and failed with latest version/s?  If SE has changed DCO SNMP agent behaviour and/or PUE Dashboard API then that would affect this.  

Cheers

Ed

(CID:146670222)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi Ed,

Thanks so much for the script. It helps us to solve a few headaches.

I have some DCO that work directly from your original script, maybe only need to edit the file via Webmin to make sure encoding follows Linux requirements. But for 3pcs DCOs I recently encountered, they only worked when I cut away the /1/ from awk commands i.e.

/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '{print $2}'|awk -F"," '{print $1}'

Is there any concern if I cut the /1/ away? Thanks a lot

Fergus Wong Daniel Kwong ben lai Michael Lam

Best regards,

Winnie

(CID:147195524)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi Ed Tarento 

im trying to configure PUE with DCE 7.8.0 and DCO 8.3.2 but i cannot see the Value on DCE

i did the test.sh and no pue value

 

with snmpwalk i cannot find .1.3.6.1.4.1.26639.1.2.0

i have followed all PDF's steps

with API https:///rest/pue-v1/instantPueData i can see the value

 where am i wrong?

 

thanks

(CID:153944595)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

Dear Gianluca Bertuletti,

From your question:

with snmpwalk i cannot find .1.3.6.1.4.1.26639.1.2.0

Have you made the necessary changes to the /etc/snmp/snmpd.conf file?

You have created the necessary /etc/snmp/getPUE.sh script as follows:

Have you restarted the snmpd service?

With respect.

(CID:153944802)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:58 PM

Hi spezialist

snmpd

here the file that i have used getPUE.sh

 

service restarted also rebooted DCO server

(CID:153944816)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:57 PM

Ok, and this /etc/snmp/getPUE.sh script is executable?

With respect.

(CID:153944831)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi spezialist

(CID:153944839)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:18 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi Gianluca Bertuletti,

Couldn't it be an encoding error of you executable files ? How did you create the .sh file ?

F

(CID:153944858)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi

created as test.sh file

i used notepad++

(CID:153944865)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

For proper testing, you need, for example, to run this script with two parameters:

./getPUE.sh -g .1.3.6.1.4.1.26639.1.2.0

or

./getPUE.sh -n .1.3.6.1.4.1.26639.1.1.0

Try it.

(CID:153944868)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi spezialist

with your test i can see the PUE

(CID:153944873)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Gianluca Bertuletti, you mean Notepad++ under Windows, and then you uploaded the file to the DCO server ? If yes, I did something very similar and it ended up not working.

I had to rewrite all the scripts by hand directly on the DCO server and using a text editor.

 

(CID:153944875)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi François

with spezialist comment i can see the PUE on DCO consolle

(CID:153944880)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Great, now show the output of the command:

systemctl status snmpd

With respect.

(CID:153944887)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi spezialist

 

(CID:153944894)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

Ok, then try the following from DCO command line:

snmpwalk -v2c -cpublic 127.0.0.1 .1.3.6.1.4.1.26639.1.2.0

or from outside:

snmpwalk -v2c -cpublic  .1.3.6.1.4.1.26639.1.2.0

I assume using SNMP v2 and public community string.

(CID:153944910)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:19 PM . Last Modified: ‎2024-04-03 11:57 PM

From the comments above regarding test.sh:

Andrew, 

Check the line in test.sh is a single line

pue=`/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '/1/ {print $2}'|awk -F"," '/1/ {print $1}' `

and not 2 lines as it show in the PDF

I'll update the doco to make this clear

Let me know how you go

(CID:153944914)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

No snmpwalk on DCO

i did a snmpwalk with DCE but no .1.3.6.1.4.1.26639.1.2.0 

Walk.txt

(CID:153944917)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

Please take a screenshot (not txt or pdf file) and attach it:

(CID:153944922)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

(CID:153944929)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

Dear Gianluca Bertuletti,

Regarding the test.sh file: make sure that you have exactly this line (spaces are important):

pue=`/bin/curl -ks https://"$DCOip"/rest/pue-v1/instantPueData| awk -F":" '/1/ {print $2}'|awk -F"," '/1/ {print $1}'`

This works fine for me:

[root@dco ~]# ./test.sh
localhost
-1.0

Regarding getPUE.sh file: this file is very simple and does not support snmpwalking of the full MIB tree (this is important). That is, snmpwalk ... enterprises, for example, will not work (you will not see what you would like). There are two ways to check the operation of this file:

[root@dco snmp]# snmpwalk -v2c -cpublic localhost enterprises.26639.1.2.0
SNMPv2-SMI::enterprises.26639.1.2.0 = STRING: "-1.0"

or

[root@dco snmp]# snmpget -v2c -cpublic localhost enterprises.26639.1.2.0
SNMPv2-SMI::enterprises.26639.1.2.0 = STRING: "-1.0"

For a DCE server, this is quite enough, since, for example, in its work it uses only snmpget requests, but not snmpwalk requests.

Hope this helps you.

With respect.

(CID:153945238)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

Hi spezialist

i did some test on my DCO Vm and now works.

for your experience, is it possible to have 2 decimals? 

now is 1.2 but in real 1.14

(CID:153945243)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

Dear Gianluca Bertuletti,

Excellent 😀.

I understand you, and I'll write here as soon as I can.

With respect.

(CID:153945526)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2024-04-03 11:57 PM

Dear Gianluca Bertuletti,

From your question:

for your experience, is it possible to have 2 decimals? 

now is 1.2 but in real 1.14

Unfortunately, the problem is on the DCE software side: for the Generic sensor type from Supplemental OIDs... menu it is impossible to specify the number of decimal places. That is, by default, only one decimal place (i.e. 1.0).

With respect.

(CID:154403349)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2023-10-22 01:26 AM

0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:20 PM . Last Modified: ‎2023-10-22 01:26 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore