DCE monitored from Nagios

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE monitored from Nagios
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:11 PM . Last Modified: ‎2024-04-09 01:32 AM

0 Likes
5
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:11 PM . Last Modified: ‎2024-04-09 01:32 AM

DCE monitored from Nagios

Hi 

I have a customer who wants  to check if his DCE server is alive from his Nagios server.

Is there any Services that he is able to check on?

Or any OID´s that can report the status of the DCE Server

Thanks

Christian 

(CID:105460110)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:11 PM . Last Modified: ‎2024-04-09 01:32 AM

0 Likes
3
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:11 PM . Last Modified: ‎2024-04-09 01:32 AM

Hi Christian,

 

DCE responds to a few Linux based OIDs. If you enable SNMP in the server access tab, you could for instance query:

.iso.org.dod.internet.mgmt.mib-2.system.sysUpTime

That will give you server up time. That will not however verify that all processes are running, only that the OS is running. 

 

You could try polling DCE using it's web API and if you can get device information, you can tell if it's both working and polling device info. The customer would have to code to this API and I don't know what options Nagios has but I tend to think that this may not be one.

 

The only other option I can think of is to create a threshold and send an e-mail. You can have it repeat at a max 1440 minutes:

 

You could do this with a trap as well but if you're using the NMS integration feature, any threshold will alert using that option as well and it won't follow the alert action scheduling.

 

Steve

(CID:105460139)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:11 PM . Last Modified: ‎2024-04-09 01:32 AM

0 Likes
3
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:11 PM . Last Modified: ‎2024-04-09 01:32 AM

Hi Christian,

 

DCE responds to a few Linux based OIDs. If you enable SNMP in the server access tab, you could for instance query:

.iso.org.dod.internet.mgmt.mib-2.system.sysUpTime

That will give you server up time. That will not however verify that all processes are running, only that the OS is running. 

 

You could try polling DCE using it's web API and if you can get device information, you can tell if it's both working and polling device info. The customer would have to code to this API and I don't know what options Nagios has but I tend to think that this may not be one.

 

The only other option I can think of is to create a threshold and send an e-mail. You can have it repeat at a max 1440 minutes:

 

You could do this with a trap as well but if you're using the NMS integration feature, any threshold will alert using that option as well and it won't follow the alert action scheduling.

 

Steve

(CID:105460139)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2024-04-09 01:32 AM

In response to DCIM_Support
0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2024-04-09 01:32 AM

Thanks Steven

This is not much but we will find a acceptable solution for the customer.

/Christian 

(CID:105460468)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2024-04-09 01:32 AM

In response to DCIM_Support
0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2024-04-09 01:32 AM

Hello, Steven! And how can I get list of those few OIDs you mentioned at the beginning of your answer?

(CID:123349147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2024-04-09 01:32 AM

In response to DCIM_Support
0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2024-04-09 01:32 AM

Hi Nikita,

 

I've actually seen them change from version to version and the number of responses has increased lately. I think it's best if you run an SNMPwalk yourself so that you can make more sense of the responses. Running 7.4.3, I've done a walk but to remove potentially sensitive info, I've removed the responses and edited other lines. I've no more info on what each line is.

 

isxcwalk.xlsx

 

Steve

(CID:123349274)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2023-10-31 10:27 PM

0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:12 PM . Last Modified: ‎2023-10-31 10:27 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore