DCE as a SNMP Gateway

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE as a SNMP Gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

0 Likes
11
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

DCE as a SNMP Gateway

Hello any possibility to use DCE as a SNMP Gateway?
Customer wants to read all Sensor Data connected to DCE and store in their BMS System. They want to periodically read the data through SNMP, they dont want to receive a SNMP trap.

 

thank you

(CID:126163629)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

0 Likes
7
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hi Sven,

 

DCE does not output any SNMP data for the devices it monitors. The only SNMP data you can receive is the OS based data CentOS outputs. DCE can output modbus data for up to 247 devices worth of data using the AP95MODBUS license key. You can not add more licenses to increase that number.

DCE's devices can be monitored using the web API. This HTTP protocol data can be found here:

 StruxureWare Data Center Expert Web Service API


Thanks,

Steve

(CID:126163638)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hello Steven and thank you,

 

What about the Netbotz device? Does the Netbotz support these functionality?

 

e.g. by downloading the MIB file and implementing in the BMS system?

https://www.schneider-electric.com/en/faqs/FA158368/

 

thank you

 

(CID:126163651)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hi Sven,

You can monitor a NetBotz device and it's sensors using SNMP. This includes any SNMP device it may be monitoring using the 5 node device monitoring pack NBWN0006. 

Steve

(CID:126163656)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hello Steven,

 

just to clarify:

 

I have a Netbotz 450 connected with 2x Bot150 

12x dry contacts an 6x apc sensors.

 

These need to be available through snmp in the BMS System.

By using the 5 node device monitoring license, only 5 from these 18 would be available in the BMS System?

 

Do I need to implement 4x NBWN0006 to have all the sensors available?

 

thx

 

(CID:126163658)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hi Sven,

 

Sorry for any confusion. No, all sensors that NetBotz are currently monitoring are available to be monitored via SNMP. This includes all sensors connected to the 150 pods. No license is required to use any system to monitor the NetBotz via SNMP.

The NBWN0006 is used if you are looking to monitor other devices via SNMP from the NetBotz appliance. For instance if you were monitoring an APC PDU using SNMP with the NetBotz device, you would need the NBWN0006. Here you can see I'm monitoring a PDU with the NetBotz 570 I have:

You could then see it's values via SNMP when monitoring the NetBotz appliance:


The NetBotz can monitor up to 5 SNMP devices total and can only have one license of this type installed per unit. Again, this is NOT necessary if you are monitoring the appliance, only if the appliance is monitoring another device. Additionally, I do not believe new DDFs are being made for this feature.

Steve

 

(CID:126163675)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hello Steve and thank you for detailed explanation.

 

One more question. I am using 2 Netbotz 450

on the first a usb gsm modem is connected. I also want to implement the devices connected to the 2nd Netbotz 450 to send and receive alarm sms.

Is this possible by using the NBWN0006 because Pod sharing is not possible at Netbotz 450 ?

(CID:126163683)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Hi Sven,

 

That license key is for a NetBotz to monitor an SNMP device. It is not used to monitor other NetBotz devices. You could try it but you'd have to add each OID manually as a supplemental OID. I've never really tried this but it could work.

 

When using a NetBotz 450, you can not even use the pod sharing feature to monitor another NetBotz appliances's sensors as you noted (you can on the 550, 570 and 455). With the 450, For the best experience, you'd want to add a modem to that unit as well.

(CID:126163702)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:32 AM . Last Modified: ‎2024-04-05 04:33 AM

Sorry, just tested it. It won't work.

I tried adding a 355 and adding a supplemental OID. First, I had to figure out the OID I wanted so here you can see that I pulled the temperature data via SNMP:

Please note the long string at the end after polling that OID(2641473744). That is the instance. If there were multiple sensors of this type, each would have a different instance. In NetBotz, the instance is always huge like this. 

When I tried adding this string as a supplimental OID as you would need to for each individual sensor, I get an error that it is an invalid OID:

I can add it without the instance but no data will be returned in advanced view.

 

Steve

 

(CID:126163705)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:33 AM . Last Modified: ‎2024-04-05 04:33 AM

0 Likes
1
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:33 AM . Last Modified: ‎2024-04-05 04:33 AM

Hi Sven.

I wonder why they want to duplicate the collected data in 2 places?  What would be the problem with the BMS people getting access to the data using the DCE (read only?) web and/or Java clients?  

Are the monitored devices on the DCE public or private NIC?  If public, have you discounted the idea of the BMS monitoring the devices directly via SNMP, i.e. bypassing the DCE altogether?  If private, you could consider connecting a second BMS NIC to the DCE private LAN and the BMS could monitor the devices directly, assuming the private LAN can be extended to the BMS and the BMS is capable (many aren't).

Another option would be the use of an intermediate gateway such as the one developed in Australia but this would require both capex and opex budgets.

Cheers

Ed 

(CID:126163877)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:33 AM . Last Modified: ‎2024-04-05 04:33 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:33 AM . Last Modified: ‎2024-04-05 04:33 AM

Apologies, my initial post read "consider connecting a second BMS NIC to the DCE private LAN".  I left out the word "NIC".  I've updated my entry.   I have not lost my marbles (well not all of them)

(CID:126164016)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:33 AM . Last Modified: ‎2023-10-22 01:23 AM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:33 AM . Last Modified: ‎2023-10-22 01:23 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore