EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 11:58 PM . Last Modified: 2024-04-04 01:15 AM
In DCE map view, you are able to show label information. Example Phase 1 Power (which is a virtual sensor I created)
I notice that when I turn off power, the virtual sensor is shown dropping slowly 2200w -> 1550w ->970w etc to eventually zero despite the true sensor value being updated from 2200 to zero on the poll.
Is there a way to set the refresh rate on these labels to update at the same pace as teh sensor(s) they rely on?
(CID:134034813)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 11:58 PM . Last Modified: 2024-04-04 01:14 AM
Hi John,
There is no way to configure the refresh rate on the virtual sensor, sorry. There is no written explanation on how the sensor arrives at it's value vs specific device polling but each device must be polled for the virtual sensor to be updated.
If you have 3 PDUs summed up for a virtual sensor for instance and the poll rate is 5 minutes, it could take up to 5 minutes before the sensor is showing the actual value. Since each device / sensor is polled at a slightly different time, that's why you get the change in reading 2200w -> 1550w ->970w etc.
Thanks,
Steve
(CID:134034827)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 11:58 PM . Last Modified: 2024-04-04 01:14 AM
Hi John,
There is no way to configure the refresh rate on the virtual sensor, sorry. There is no written explanation on how the sensor arrives at it's value vs specific device polling but each device must be polled for the virtual sensor to be updated.
If you have 3 PDUs summed up for a virtual sensor for instance and the poll rate is 5 minutes, it could take up to 5 minutes before the sensor is showing the actual value. Since each device / sensor is polled at a slightly different time, that's why you get the change in reading 2200w -> 1550w ->970w etc.
Thanks,
Steve
(CID:134034827)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 11:58 PM . Last Modified: 2024-04-04 01:14 AM
Dear John Lales,
Tell us, please, did you solve your question or not?
With respect.
(CID:134679982)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 11:58 PM . Last Modified: 2023-10-22 01:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.