Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-22 01:41 AM
Hi All
I am performing a DCE VM Server upgrade for a client from v7.8.1 to v7.9.3. I have followed the correct upgrade procedure however the DCE v7.9.3 cannot see the Backup created by the DCE Server v7.8.1.
Both Servers have the same Mac Address and Hostname (Only one server runs at a time) and they are both running their Backups into the same Share Folder however they can only see the Backup they individually created i.e the Server v7.8.1 only sees its back and the same for v7.9.3 but the Backups are sitting in the same Share Folder.
I ran my backups using NFS and TCP Protocol.
Anyone with any advice on how to resolve this?
Please see screenshots attached.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-25 06:21 AM
Hello,
you cannot upgrade directly to 7.9.3...you must use .ova version 7.9.0 and then update to 7.9.1, 2, 3
Backups from 7.8.1 are compatible only with version 7.9.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-26 12:30 AM
Hi @Gabi
Thank you for your response. Much appreciated!
Will try this method and revert with feedback!
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.