DCE SNMP v3 configuration for ABB Conceptpower UPS

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE SNMP v3 configuration for ABB Conceptpower UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

0 Likes
12
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

DCE SNMP v3 configuration for ABB Conceptpower UPS

I have 4 same model ABB UPS. 3 snmpv1. I ran walkfile and ddf file received worked fine.

3rd UPS interface interface was replaced for a new one (older is not supported now) it just supports snmpv2 and snmpv3. I configured snmpv3 (no password/no encription) and ran walkfile. With ddf received,  UPS is not discovered.

I have tried configuring authentication both on UPS and DCE and UPS is not discovered.

I have also tried configuring v2 on UPS and v1 on DCE and UPS is not discovered.

Help please  

(CID:110010413)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

0 Likes
2
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

Hi Oscar,

 

What version of DCE are you running? 

Have you tried discovering any other devices using SNMP version 3 with that specific DCE?

Does the UPS' network card report when invalid security is used? For instance, an APC network management card will log errors when a system tries to connect to it using incorrect SNMP credentials. If this device can do that as well, we can at least verify that the get requests are getting to the device.

Is there a way you could run a packet capture at the DCE server side of the network to verify it is sending the correct info and in turn receiving it as well?

This knowledge base document FA226273 might also be helpful in troubleshooting this issue.

 

Thanks,

Steve.

 

(CID:110010547)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

Hi, I am using DCE 7.4.1. I have no other device using SNMPv3. There is no logs on UPS about security issues.

I have not tried to capture traffic. However, every device is in the same subnetwork and they use the same port for SNMPv1 traffic, so it should work with no problems. We ran walkfile tool to get mib configuration on v3 and it worked fine

(CID:110011638)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

Hi,

DCE 4.7.1

There is no other SNMP v3 device to discover, so I cannot test it

UPS does not report any error or log

I have not way to access to the network to filter the traffic. I should ask my customer to try.

On other link (on conceptpower device support) I have passed the following information:

Hi, actually there is no error. just the device is not found. Attached you have screenshots of detection panel and the device is not added to the list. IP address is 10.253.113.242. I have tried configuring snmp on  v1 and v3 on DCE (v2 and v3 on UPS). On devices list you can see the 3 UPS found because their interface runs snmp v1

(CID:110011640)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

0 Likes
7
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:23 AM . Last Modified: ‎2024-04-08 03:33 AM

On my devices request (concptpower) I received an answer that snmp v3 is not supported on  DCE v7.4.1. However manual says snmp v 1 and snmp v3 are supported, and there are options on device seach to select one version or the other. Moreover, the dev_walk.cmd has options to search on v1 or v3 snmp devices. I got walkfiles using it, and then a ddf was sent to me.

I am not able to write an answer to that comment. I have escalated it to my local Schneider contact, but they have not got answer yet. Any place where it is reported snmp v3 is nor supported? or any idea for next steps? 

(CID:110791833)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

Hi Oscar,

 

Do you have a link to that comment so I can check it out? SNMP version 3 is absolutely supported in all versions of DCE.

 

Steve

(CID:110791934)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

Sure: https://dcimsupport.apc.com/devices/requests

it is in my device requests, at Conceptpower device. I don't know if you can access the link

 

(CID:110791993)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

No, sorry. That brings me to my own requests.

Screenshot?

 

Steve

 

(CID:110792007)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

here is the images of the conversation. Last image is the test they did with ddf file with snmpv1

(CID:110792019)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

Right now I just wanted to verify who was telling you we didn't support SNMP version 3 and make sure they understand that we do. I have forwarded this thread to the appropriate people to address that.

 

As for not being able to discover, this thread seems to have gone on for some time. I'm wondering if direct phone contact with technical support may not lead to a quicker resolution. If SNMP version 1 works, we know it's not the DDF. It would then be either the configuration of the device, of DCE, or an issue with one of the 2. Testing with SNMP version 3 with and without some of the extra protocols may help.

 

Steve

(CID:110792033)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

oscar dafauce did you try out Steve's suggestion, and did it solve your issue ?

(CID:111412997)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

In response to DCIM_Support
0 Likes
0
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2024-04-08 03:33 AM

I have contacted my local commercial contact but unfortunately, I have not got it solved yet. Thanks

 

(CID:111413026)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2023-10-22 01:19 AM

0 Likes
0
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:24 AM . Last Modified: ‎2023-10-22 01:19 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore