DCE: SNMP device not showing sensors

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE: SNMP device not showing sensors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
9
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

DCE: SNMP device not showing sensors

Hello support,

 

I need advice on a DCE installation that involves the integration of 3rd party SNMP devices.

 

We went through the process to develop the ddf (xml) for the snmp gateway (the device is a Genset) and insert the ddf to DCE with success, but when the device is added it only shows as "SNMP Device", without any sensor.

 

It looks like the device type is not being recognized.

 

The reference for the DDF development process was DDF-2233.

 

I thank you for any help on this matter.

 

 

(CID:119637802)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
1
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi Rafael,

From the reference number DDF-2233, I can see that due to some reason a WALK could not be generated and it was agreed upon that we would be unable to test the DDF without the WALK file.

To debug this issue, we could go about it in the following way:

  • Provide a WALK file so that we can simulate it and find out what the issue could be.
  • Contact the device vendor and obtain the correct OID list. With this we can cross reference the DDF to check if the OID's used in the DDF are correct.

Regards,

Divya Shankar

(CID:119638047)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi rafael.pereira,

Maybe my question will be simple, but I want to ask: Is your DDF-file for an SNMP-device or for a Modbus-device?

Maybe DDF-file is created for the Modbus-devices (Genset), which is connected to the DCE-server via Modbus TCP/IP gateway?

In this case, discovering the Modbus TCP/IP gateway only by its IP-address on the DCE-server as an SNMP-device will result in the result described by you, i.e. without any sensors. In this case, on your DCE-server, your Genset should be discovered as a Modbus-device, specifying the IP-address of the Modbus TCP/IP gateway and the SlaveID of your Genset.

With respect.

(CID:119637854)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
1
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi Rafael,

From the reference number DDF-2233, I can see that due to some reason a WALK could not be generated and it was agreed upon that we would be unable to test the DDF without the WALK file.

To debug this issue, we could go about it in the following way:

  • Provide a WALK file so that we can simulate it and find out what the issue could be.
  • Contact the device vendor and obtain the correct OID list. With this we can cross reference the DDF to check if the OID's used in the DDF are correct.

Regards,

Divya Shankar

(CID:119638047)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

In response to DCIM_Support
0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:28 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi Divya,

 

That comment was on DDF-2155 thread and was misplaced, as i informed some comments after that. The system that failed the SNMP walk was the air conditioner gateway treated on de DDF-2233. That one is subject to the other question I´ve opened yesterday (the one that is not being discovered by DCE).

 

For this one, the Genset Gateway, we got the SNMP Walk response. The device is already discovered by the DCE, but shows no sensors.

 

I´ll run another SNMP Walk, anyway, to update you.

 

 

(CID:120129290)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

Hello, 

 

Thank you for the comment! No problem to review the basics in my POV.

But it´s indeed a SNMP DDF. The file itself is a xml that was successfully imported to DCE as a DDF for SNMP.

 

Best regards.

 

 

(CID:120129293)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi rafael.pereira,

Thank you for understanding 😀. Just in my practice there have been numerous cases where people ordered a Modbus DDF-file, then successfully imported it into DCE-server. And then tried unsuccessfully to perform discovering of Modbus TCP/IP gateway as SNMP-device 😀.

Now regarding your question: I have several times seen similar problems, and I want to ask: after the discovery on DCE-server of your SNMP-device, it remains in online state or go to offline (in a minute or two)? Can show a screenshot of the discovered SNMP-device and its "sensors"?

Always glad to help.

(CID:120129348)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi @spezialist,

 

I´ve just checked and the state remains "normal".

 

I couldn´t take the screenshot although.

(CID:120129660)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi rafael.pereira,

And again, have you solved the problem or not?

With respect.

(CID:120131776)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2024-04-08 12:37 AM

Hi spezialist,

Solved yesterday. It turned out to be a problem with the DDF. After the new were generated and imported the sensors showed up.

(CID:120131780)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2023-10-22 01:19 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:29 PM . Last Modified: ‎2023-10-22 01:19 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore