DCE Auto Discover Modbus TCP Slaves? Is there a way for DCE to auto discover all slaves on a given IP address? I'm having to do this manually for hundreds of Branch Circuit Monitors and it's painful. Would save me and my team many hours of mind numbing labor:-)
(CID:131336805)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:23 PM . Last Modified: 2024-04-04 11:56 PM
Hey Greg,
Sorry, no, there is not. Due to the fact that every device / slave on any given IP can be a different device and with Modbus in DCE you can not auto-detect which DDF to use, the devices must be added individually.
Steve
(CID:131336855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:23 PM . Last Modified: 2024-04-04 11:56 PM
Hey Greg,
Sorry, no, there is not. Due to the fact that every device / slave on any given IP can be a different device and with Modbus in DCE you can not auto-detect which DDF to use, the devices must be added individually.
Steve
(CID:131336855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:23 PM . Last Modified: 2024-04-04 11:56 PM
Okay:(
(CID:131959847)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:23 PM . Last Modified: 2023-10-22 01:14 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.