DCE 7.9.2 Backup restore

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE 7.9.2 Backup restore
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
silvio.filho
Ensign silvio.filho
Ensign

Posted: ‎2023-04-06 08:13 AM

0 Likes
3
966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 08:13 AM

DCE 7.9.2 Backup restore

Hello people

 

I`m trying to make a restore from a existing backup in DCE 7.9.2 but, i can`t mount the share.

 

The original backup was made in DCE 7.8.0 and the mount run`s normaly.

 

Using the same configs in 7.9.2 i cant do this.

 

All my trys of mount dont appears on logs only the tryings of restore and in log it apperas trying to connect in port 0 what is very weird.

 

Can anyone help me please?

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2023-04-06 08:59 AM

0 Likes
0
961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 08:59 AM

Hello,

Unfortunately the migration to DCE 7.9 requires using version DCE 7.8.1 and 7.9.0, you cannot go from 7.8.0 to 7.9.2 directly.

You need to first upgrade DCE to 7.8.1, then deploy a new DCE 7.9.0 VM, if possible it is highly recommended, if not required, to use the same mac address from the old 7.8.0 server.

There is a complete 7.9.x migration guide here https://dcimsupport.ecostruxureit.com/hc/en-us/articles/4408917042577-Complete-upgrade-process-for-D...

Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Lieutenant Gabi
Lieutenant

Posted: ‎2023-04-07 06:42 AM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 06:42 AM

also, if is a windows share after backup disable SMB v1....DCE use SMB v2 now

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2023-04-07 07:15 AM

1 Like
0
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 07:15 AM

Yes, DCE 7.9.x and higher can use SMB v2/v3, only DCE 7.8.1 and below requires SMB v1.  Also when you go to restore your 7.8.1 backup on 7.9.0, make sure you change the security type to NTLMv2.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore