DCE 7.3.1 SNMPv3 Communication Issues

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE 7.3.1 SNMPv3 Communication Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

0 Likes
4
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

DCE 7.3.1 SNMPv3 Communication Issues

I am trying to setup a AP9631 with SNMPv3 but DCE loses communication with the devices once they are on SNMPv3.  The AP9631 is running version 6.4.0 and the DCE is able to connect to it when SNMPv1 is enabled.  Are there SNMPv3 settings I am missing to setup on the DCE?  Thanks

(CID:108827853)

Labels
  • Labels:
  • Data Center Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

0 Likes
1
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

Hi Rusty, 

 

If you've discovered the AP9361 with SNMP version 1 and are now changing to SNMP version 3, you must make that change using the APC SNMP device configuration options. If you simply log into the device and change the SNMP settings, you will lose comm. There is no way to directly change the SNMP configuration DCE uses to poll the device other than this option or deleting the device and re-adding it via SNMP version 3.

 

To make sure you're configuring the device correctly through DCE, please use the procedure outlined in this knowledge base document.


Thanks,

Steve

(CID:108827855)

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

0 Likes
1
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

Hi Rusty, 

 

If you've discovered the AP9361 with SNMP version 1 and are now changing to SNMP version 3, you must make that change using the APC SNMP device configuration options. If you simply log into the device and change the SNMP settings, you will lose comm. There is no way to directly change the SNMP configuration DCE uses to poll the device other than this option or deleting the device and re-adding it via SNMP version 3.

 

To make sure you're configuring the device correctly through DCE, please use the procedure outlined in this knowledge base document.


Thanks,

Steve

(CID:108827855)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

In response to DCIM_Support
0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

Thanks Steve.  I was able to locate the settings.

(CID:108827975)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:46 AM . Last Modified: ‎2024-04-08 10:41 PM

Hi Steven,

Currently, we upgrated the DCE version from 7.3.1 to 7.4.1 and we have the same issue previously reported.

Before the upgrade, the devices were added via SNMPv3 and when the upgrade finished all devices lossed the comunication.

We deleted the devices and then re-adding one by one, but the error persist.

On the other hand, the DDF file is succesfully transfered via SNMPv1, but through SNMPv3, the device is added as a SNMP device on failure state without DDF.

We appreciate your help.


 

(CID:114821004)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:47 AM . Last Modified: ‎2023-10-22 01:10 AM

0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:47 AM . Last Modified: ‎2023-10-22 01:10 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of