I have a some generators that i want to monitor using DC Expert, i installed Deep Sea Controllers, DSE 7320 with Modbus capability, i also installed TSXETG100POE gateway to convert Modbus to TCP/IP. I can see the gateway on DC Expert, but i can't read meaningful values from there.
I would appreciate some help
(CID:97485825)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:18 PM . Last Modified: 2024-04-09 04:36 AM
Dear James,
In order for you to see the Modbus device values in DCE, you need to upload the Modbus DDF files. To receive the Modbus DDF files, please send an email to Multivendorsupport@schneider-electric.com or multivendorsupport@apc.com
You will need to fill in the request form(it will be shared by multivendorsupport team) with all the required details so that they can create the DDF file and send it across to you.
To import:
Main menu->Device->Modbus Device Communication Settings->Device Definition Files->Add/Update Definitions
I hope this helps.
regards,
Bala
(CID:97485829)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:18 PM . Last Modified: 2024-04-09 04:36 AM
Dear James,
In order for you to see the Modbus device values in DCE, you need to upload the Modbus DDF files. To receive the Modbus DDF files, please send an email to Multivendorsupport@schneider-electric.com or multivendorsupport@apc.com
You will need to fill in the request form(it will be shared by multivendorsupport team) with all the required details so that they can create the DDF file and send it across to you.
To import:
Main menu->Device->Modbus Device Communication Settings->Device Definition Files->Add/Update Definitions
I hope this helps.
regards,
Bala
(CID:97485829)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:18 PM . Last Modified: 2024-04-09 04:35 AM
Thanks very much Balaraman, let me try that.
(CID:97485846)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:18 PM . Last Modified: 2023-10-31 10:45 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of