Custom DDF Files

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Custom DDF Files
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:02 AM . Last Modified: ‎2024-04-05 03:07 AM

0 Likes
3
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:02 AM . Last Modified: ‎2024-04-05 03:07 AM

Custom DDF Files

Dear Scheider Team.

We have two industrial automatic transfer switches for our Data Center, they each have an internal UPS (SMART-UPS 1500) which have an SNMP card with dry contacts in order to extract the automatic transfer switch signals.

 

The issue is that the OIDs on the ddf file of the previously mentioned UPSs only return contact states (open/closed)

 

Is there a way to customize the ddf file so that the OIDs return specific states? e.g., the OID indicating Utility/Generators instead of Open/Closed.

 

Than you.

(CID:128065443)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:02 AM . Last Modified: ‎2024-04-05 03:07 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:02 AM . Last Modified: ‎2024-04-05 03:07 AM

Dear Banco Central Honduras,

Since you are using Schneider Electric's native UPS, customizing DDF-files in this case is simply not possible for obvious reasons.

Therefore, firstly, it is recommended for your dry contacts in the NMC to change their Name and Location so that their purpose is clear.

Secondly, in the DCE software for these dry contacts in the Threshold Alarm Configuration view, you need to configure the corresponding custom alarm thresholds, since you already need it, i.e. Utility/Generators, etc. How to do this is written, for example, in Threshold Alarm Configuration view and can be seen in the video Creating and Managing Thresholds in StruxureWare Data Center Expert.

In addition, I recommend to you after this in the settings of your NMC to disable the alerting about the change status of the used dry contacts. If you do not, then when dry contacts are triggered, the DCE-server will generate two alarms, which will duplicate each other. One alarm will be, that the state of the dry contacts has changed (this is standard Device Alarm), and the second alarm will be about what happened, for example, starting generators or other (this is custom Threshold Alarm).

I hope this is what you need.

If you have any questions, please ask.

With respect.

(CID:128065487)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:02 AM . Last Modified: ‎2024-04-05 03:07 AM

0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:02 AM . Last Modified: ‎2024-04-05 03:07 AM

Dear Banco Central Honduras,

Since you are using Schneider Electric's native UPS, customizing DDF-files in this case is simply not possible for obvious reasons.

Therefore, firstly, it is recommended for your dry contacts in the NMC to change their Name and Location so that their purpose is clear.

Secondly, in the DCE software for these dry contacts in the Threshold Alarm Configuration view, you need to configure the corresponding custom alarm thresholds, since you already need it, i.e. Utility/Generators, etc. How to do this is written, for example, in Threshold Alarm Configuration view and can be seen in the video Creating and Managing Thresholds in StruxureWare Data Center Expert.

In addition, I recommend to you after this in the settings of your NMC to disable the alerting about the change status of the used dry contacts. If you do not, then when dry contacts are triggered, the DCE-server will generate two alarms, which will duplicate each other. One alarm will be, that the state of the dry contacts has changed (this is standard Device Alarm), and the second alarm will be about what happened, for example, starting generators or other (this is custom Threshold Alarm).

I hope this is what you need.

If you have any questions, please ask.

With respect.

(CID:128065487)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:03 AM . Last Modified: ‎2024-04-05 03:07 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:03 AM . Last Modified: ‎2024-04-05 03:07 AM

Thank you

(CID:128067958)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:03 AM . Last Modified: ‎2023-10-22 01:07 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:03 AM . Last Modified: ‎2023-10-22 01:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore