Correct Power Path Setup

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Correct Power Path Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

0 Likes
7
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

Correct Power Path Setup

Looking for some advice on how to correctly model a power setup.

There is one LV input that has a separate feed to two UPS units A and B.

The two UPS's output on to a common busbar which in turns connects to three separate floor PDUs.  Rack power strips are then connected to the floor PDUs.

I have currently modelled this in DCO as follows,

 

 

I then have rack power strips connected to the relevant breakers in the floor PDUs with in rack device redundancy set to DN+1.

Is this correct?

(CID:133374306)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

0 Likes
2
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

Hi James,

I think it depends on UPS internal redundancy settings.

a) If UPS internal redundancy is N+1, then the rack device redundancy may be

Distribution redundancy N+1 (if connected to two rack pdus)

or N+1 (if connected to one rack pdu)

b) If UPS internal redundancy is N, then the rack device redundancy may be

Distribution redundancy N (if connected to two rack pdus)

or N (if connected to one rack pdu).

Kind regards

(CID:133374377)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

In response to DCIM_Support
0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

Jef Faridi - Thanks for the reply.  There are two rack power strips per rack with each device connect to both.  Aside from the redundancy of the in rack devices is the general power path correct?  Or is there a better way to represent it?

(CID:133374398)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

In response to DCIM_Support
0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

Hi James,

I have restudied the description, I don't think connecting two power sources (UPS A and B) to Busbar (apparently ats/sts device) is supported in DCO.

I think the best workaround could be only connect one UPS to Busbar (modeled as PDU), and increase the UPS capacity to the total available capacity (UPS A + UPS B).

Kind regards

(CID:133374852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

0 Likes
2
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:02 PM . Last Modified: ‎2024-04-04 03:28 AM

Hi James,

 

General speaking, a given power infrastructure can be utilized in different ways, which is why DCO has additional  settings on UPS, rack, server, etc; they are there so you can tell DCO how you intend to utilized your power infrastructure.

Which means, for a given setup there is not just one correct setting, it all boils down to what you want to active.

So, when you are asking if your the setup is correct, the answer is going to be: yes AND no, it depends on why the power infrastructure is designed this way, that is, how do you intend to utilized it?

A1) Considering the 2 UPS's connected to a busbar, normally this means that they work in parallel and both shares the load. Do you intend to use the full capacity of the 2 UPS's or is it a redundancy setup where one UPS should be able to handle the entire load?

A2) Does the 2 UPS's have internal redundancy, e.g. some =SE= UPS's has a number of power modules where one can be considered as redundant.

B) Why are there 2 rackPDUs in the rack, is it because you need more power capacity in the rack than one rackPDU can deliver? Or is it because you want redundancy at rackPDU level, i.e. one rackPDU is enough to power all equipment in the rack?

Once you have answered these questions we (Jeff or me) can come up with some recommendations on how to model/configure your power path in DCO.

Best,

Gert

 

(CID:133375572)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:03 PM . Last Modified: ‎2024-04-04 03:28 AM

In response to DCIM_Support
0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:03 PM . Last Modified: ‎2024-04-04 03:28 AM

Gert Lehmann - To answer your questions

A1 - They are intended to be used in a redundant setup.  One UPS should be able to take the whole load.

A2 - There is no internal redundancy in the 2 UPS's

B - This is for redundancy at rack level - each device is connected to both rack PDUs.

(CID:133375639)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:03 PM . Last Modified: ‎2024-04-04 03:28 AM

In response to DCIM_Support
0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:03 PM . Last Modified: ‎2024-04-04 03:28 AM

OK, in that case I would recommend the following:

A) DCO is not able to model busbar/parallel-ups and the normal "work around" is to model just one UPS with N+1 and specifying the capacity without the "+1" UPS - e.g. if you have 2 x 1 MW then then capacity is 1 MW.

Since there are only 2 UPS's, your setup with an ATS would also work, but it that case the UPS redundancy would be N (since you have modeled the "+1" using an ATS) and each UPS should have their full capacity (e.g. 1 MW each).

B) The "Infrastructure requirements redundancy" on equipment in the racks should be "DN+1" if you setup the UPS as "N+1", otherwise is should be "DN" - the reason I asked is beacsue people has a tendency to connect devices to both rackPDUs even when they want to utilize the full capacity (N).

Best,

Gert

(CID:133375912)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:03 PM . Last Modified: ‎2023-10-22 01:07 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:03 PM . Last Modified: ‎2023-10-22 01:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of