Cooling simulation failure

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Cooling simulation failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

0 Likes
5
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

Cooling simulation failure

Hello,

we have a design with hot aisle containment. The customer has realized that in the cooling simulation, selecting Velocity Plane, it seems that DCO 8.2.2 does not take the coantainment in mind when it makes the simulation.

In Temperature Plane, it does not happen:

And this is the layout in 2D:

 

(CID:129412143)

Labels
  • Labels:
  • Data Center Operation
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

Hi team,

any idea about this issue?

Regards.

(CID:130091576)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

0 Likes
2
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

Hi Javier,

Some time ago we had a similar discussion with our development team (and code reviewing), it turned out that this is working as designed.

To explain it we can look at a more simple setup, we have a room with one CACS and a downflow crac supplying the tiles inside the CACS. If the CACS outputs 13.000 m3 pr hour. that air needs to get out of the tiles and the leakage in the room. The leakage is default set to 30%, leaving 9100m3 for the tiles in the CACS. The air entering the CACS also need to leave the CACS to ensure we don't get an over-pressure in the CACS. The racks can only use a certain amount of air determined by the load in the rack multiplied with the cfm/kw property on the rack. The air not used by the racks needs to get out of the containment system through leakage, here we have 2 possibilities either through leakage in the roof or through the racks. Our implementation uses the roof.

Kind regards

(CID:130091719)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

In response to DCIM_Support
0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

Hi Jef,

but in this case we have a HACS instead of a CACS, so I think we should not have hot air entering the containment through the roof, should we?

Regards

(CID:130091771)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

In response to DCIM_Support
0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2024-04-05 12:28 AM

Hi Javier,

Using the roof in implementation is similar both for HACS and CACS.

Kind regards

(CID:130091774)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2023-10-22 01:07 AM

0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:45 PM . Last Modified: ‎2023-10-22 01:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of