Dear Team,
KIndly assist on the configuration of the AP9635CH NMC to 66061 Jbus/Modbus card on G5500 UPS.
This cards came separately from the UPS and after the physical connection of the two cards on the UPS, AP9635CH cannot load up the UPS values as shown.

Regards,
Felix
(CID:96764813)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:44 PM . Last Modified: 2024-04-09 11:44 PM
Hi Felix!
You need to properly configure UPS settings and Modbus communication between cards.
Contact your local tech support for futher assistance.
(CID:96764838)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:44 PM . Last Modified: 2024-04-09 11:44 PM
Hi Valentin, Well noted, thanks. Regards, Felix
(CID:96765097)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:44 PM . Last Modified: 2024-04-09 11:44 PM
Hi Felix,
66061 us default setting, check RS485 wiring ?
Dominique
(CID:96764844)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:44 PM . Last Modified: 2024-04-09 11:44 PM
Hi Dominique, Thanks for your contribution, I got it working. Regards Felix
(CID:96765096)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:44 PM . Last Modified: 2023-10-31 10:21 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.