Cannot connect 2x ATS switches to Rack PDUs
In some or our racks we have 2x APC ATS switches powered from a pair of Rack PDUs. In ITA I can connect 1x ATS to a pair of Rack PDUs (input power) but I cannot connect a 2nd ATS, the error is rack is already supporting an ATS. Is there a way to connect a 2nd ATS in ITA?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-0805:05 AM
Hi Setta,
By design only one rack ATS can be connected to a par of rack-pdus (inside a rack) - the limitation is due to power capacity calculations behind the scenes.