Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Can you please let let me know how to rectify this error. "The current value of Power - Bank 1 (575 W is too high
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-0208:27 AM. Last Modified: 2024-04-1001:30 AM
Hi Craig,
It appears that you have a threshold violation on your Data Center Expert. Please log into your Data Center Expert and locate the Rack PDU with the alarm.
When the device is located select Alarm Configuration in the top bar. Now select Thresholds Alarm configuration in the new window. You will know see a list of Thresholds defined on the device.
It looks like an Max alarm threshold is set to low on this device.