Can StruxureWare DCE, DCO and Portal be deployed in Cisco UCS Server ?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Can StruxureWare DCE, DCO and Portal be deployed in Cisco UCS Server ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

0 Likes
3
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

Can StruxureWare DCE, DCO and Portal be deployed in Cisco UCS Server ?

Dear Team,

 

We just got a confirmation from a Client is Bahrain that they have arranged a Cisco UCS Server for StruxureWare DCE, DCO and Portal deployment with Vmware Set Up with the attached specification.

Can the DCE, DCO and Portal be deployed in the below Server Specs.xlsx :

Line Number Part Number Description
2.0 UCSC-C220-M4S UCS C220 M4 SFF w/o CPU, mem, HD, PCIe, PSU, rail kit
2.0.1 CON-SNT-C220M4S SNTC-8X5XNBD UCS C220 M4 SFF w/o CPU, mem, HD
2.1 UCS-CPU-E52630D 2.40 GHz E5-2630 v3/85W 8C/20MB Cache/DDR4 1866MHz
2.2 UCS-MR-1X322RU-A 32GB DDR4-2133-MHz RDIMM/PC4-17000/dual rank/x4/1.2v
2.3 A03-D300GA2 300GB 6Gb SAS 10K RPM SFF HDD/hot plug/drive sled mounted
2.4 UCS-HD12TB10K12G 1.2 TB 12G SAS 10K RPM SFF HDD
2.5 UCSC-PCIE-IRJ45 Intel i350 Quad Port 1Gb Adapter
2.6 UCSC-CMAF-M4 Reversible CMA for C220 M4 friction & ball bearing rail kits
2.7 UCSC-RAILB-M4 Ball Bearing Rail Kit for C220 M4 and C240 M4 rack servers
2.8 UCSC-PSU1-770W 770W AC Hot-Plug Power Supply for 1U C-Series Rack Server
2.9 CAB-9K10A-UK Power Cord, 250VAC 10A BS1363 Plug (13 A fuse), UK
2.1 N20-BBLKD UCS 2.5 inch HDD blanking panel
2.11 UCSC-HS-C220M4 Heat sink for UCS C220 M4 rack servers
2.12 UCSC-MLOM-BLK MLOM Blanking Panel
2.13 VMW-VSP-STD-3A VMware vSphere 6 Standard (1 CPU), 3-yr, Support Required
2.13.0.1 CON-ISV1-VSXSTD3A VSphere Standard for 1 CPU; ANNUAL List 3-YR Reqd
2.14 UCSC-MRAID12G Cisco 12G SAS Modular Raid Controller
2.15 C1UCS-OPT-OUT Cisco ONE Data Center Compute Opt Out Option
     

(CID:105471106)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

0 Likes
1
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

Hi Dhiman

It should be possible to run the DCO and DCE on VMware, as long as the minimum requirements are met for each software.

Only concern is that DCO and DCE will share the cores and memory of the one server you listed, so if i.e DCE are using a lot of resources to scan a lot of devices the DCO server might be affected.

Hope that helps

Jesper Thomsen

 

(CID:105471114)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

0 Likes
1
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

Hi Dhiman

It should be possible to run the DCO and DCE on VMware, as long as the minimum requirements are met for each software.

Only concern is that DCO and DCE will share the cores and memory of the one server you listed, so if i.e DCE are using a lot of resources to scan a lot of devices the DCO server might be affected.

Hope that helps

Jesper Thomsen

 

(CID:105471114)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

In response to DCIM_Support
0 Likes
0
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2024-04-09 12:25 AM

Dear Jesper, Thanks a lot for the prompt response. I will make sure that the Client is aware of the utilization of the CPU with regards to the three applications. As of now there will not be too much of traffic in the DC Expert as the solution is for only 50 Racks with 10 Rack PDUs and 2 UPS. Total nodes will be around 20. Thanking you once again and wishing you a great day ! Regards, Dhiman Das

(CID:105471120)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2023-10-31 10:19 PM

0 Likes
0
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:00 AM . Last Modified: ‎2023-10-31 10:19 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore