Ive just entered a load of servers into a rack in DCO.
The racks physical power limit is 24.54kW (
estimated load is 9.55kW
Potential Failover load is 9.32kW
Im at a loss to understand what this error means with these figures ?
thanks
(CID:106891457)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:41 AM . Last Modified: 2024-04-08 11:35 PM
The mentioned recommendation looks a the breaker limit for each power phase on each rack PDU, and will show up if the estimated load + failover load on that particular breaker exceeds the limit.
E.g. if you have a rack with 1 three phase rack PDU and connected all servers to L1, then you have exceed the breaker capacity of L1 at 1/3 of the total rack capacity.
(CID:106891475)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:41 AM . Last Modified: 2023-10-31 10:17 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.