We had a power loss alert from one of our UPS's that is being monitored in DCE. The gent who was on shift at the time received the email from the UPS but when he checked it in DCE the folder was still showing green. See the screen grab below for details.
(CID:105470842)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:55 AM . Last Modified: 2024-04-09 12:27 AM
Hi Matthew,
If you check the UPS logs, how long did the actual on-battery event last?
I you check DCE under the device menu -> SNMP device communications settings -> Device scan settings, select the UPS in question and hit the button for "Edit Device Scan Settings...", Is this device configured for priority scanning?
Is the write community name correct?
What is the scan interval? If it is default, cancel out of this window and back to the SNMP device settings window. Click global scan settings. What is the global scan interval?
You may also want to check the Alarm Configuration perspective under device alarm configurations. Select that Smart-UPS 2200 on the left and check the device alarms to verify they are enabled. In this case, maybe check the UPS on battery under the battery alarms. Verify it's severity and that it is enabled.
Steve
(CID:105470854)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:55 AM . Last Modified: 2023-10-31 10:14 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of