After reinstalling the system, import the backup file to restore the data, ETL does not work properly

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • After reinstalling the system, import the backup file to restore the data, ETL does not work properly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:26 PM . Last Modified: ‎2024-04-07 11:52 PM

0 Likes
9
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:26 PM . Last Modified: ‎2024-04-07 11:52 PM

After reinstalling the system, import the backup file to restore the data, ETL does not work properly

etl5.logDCO ETL.docx

(CID:123340833)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:26 PM . Last Modified: ‎2024-04-07 11:52 PM

0 Likes
1
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:26 PM . Last Modified: ‎2024-04-07 11:52 PM

Hi,
After restoring, ETL database is Paused automatically, We have to start it manually through webmin - ETL integration mgmt page.

Refer Screenshot

 

(CID:123340880)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:26 PM . Last Modified: ‎2024-04-07 11:52 PM

In response to DCIM_Support
0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:26 PM . Last Modified: ‎2024-04-07 11:52 PM

Manual start, run ETL will be an error.

(CID:123340915)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:52 PM

0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:52 PM

Hi

If you've check the DB via webmin and tried to start as advised by Rashmi and got an error, drop the External System via DCO GUI then the DB then recreate the DB via webmin and then recreate the External System via DCO GUI)

Ed

(CID:123340919)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

0 Likes
4
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

Hi xpower123

After a restore the custom transformation files are not restored to the correct location. They have to be copied from the /data/pentaho_restore/import folder to the /data/pentaho/import folder. In a cluster the /data/pentaho_restore folder is located on the server that initiated the restore, and the files have to be copied to all servers in the cluster.

Regards,

Ulrik

(CID:123342195)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

In response to DCIM_Support
0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

Hi xpower123

Would it be possible for you to share the server log files? They can be downloaded via the Webmin console on port 10000?

Regards,

Ulrik

(CID:123342785)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

In response to DCIM_Support
0 Likes
0
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

The attachment is a log of ETL runs  etl1.log

(CID:123342790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

In response to DCIM_Support
0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

Hi xpower123

The log file indicate that the BMS login to DESIGO is invalid. Could you check the instance, database, username and password settings?

It seems you have re-uploaded the database driver and added the import transformations to /data/pentaho/import folder.

There might be other issues, but they would then be logged in the server.log file. Note: the complete set of log files can be downloaded in Webmin -> StruxureWare DC Operation -> Download Log Files.

Regards,

Ulrik

(CID:123342795)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

In response to DCIM_Support
0 Likes
0
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2024-04-07 11:51 PM

Hi Ulrik,

we test for days, the ETL can get the latest data from BMS, but another issue come out.

It seems that all rackpdu data lost, so that it can't calculate PUE.

you can find the issue in the picture below, the pdu shows "associated device data has been lost"

Do you think this issue is related to the wrong ETL file? becase the ETL file has been modified many times, so after we restore the DCO, we asked for a latest set of ETL script,  didn't use the one we used before. but this 2 set of ETL come from the same person. Hope this information will be helpful .

(CID:123344428)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2023-10-20 04:59 AM

0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:27 PM . Last Modified: ‎2023-10-20 04:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore