Adding netbotz sensors into DCE default notification policy

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Adding netbotz sensors into DCE default notification policy
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:51 PM . Last Modified: ‎2024-04-05 12:06 AM

0 Likes
3
692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:51 PM . Last Modified: ‎2024-04-05 12:06 AM

Adding netbotz sensors into DCE default notification policy

Good day all

Please assist

We would like to add netbotz 550 external sensors to the default notification policy. Is there anyway that we can do that? i would like to set thresholds and customise each sensor.

Is this possible.

Currently, i have configured these settings by right clicking the device - netbotz appliance configuration>Alert thresholds> and selecting  sensors. After following all the prompts i do not receive e-mails. I presume that these sensors are not in the default notification policy.

Any suggestions.

Your assistance is much appreciated

(CID:130098889)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:51 PM . Last Modified: ‎2024-04-05 12:06 AM

0 Likes
0
692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:51 PM . Last Modified: ‎2024-04-05 12:06 AM

Dear juice,

In general, NetBotz-4.x appliance is absolutely independent device from DCE-server.

This means, that in order for you to be able to receive any notifications about the status of external sensors, that are connected to particular NetBotz-4.x appliance, all the relevant settings need to be done on this particular NetBotz-4.x appliance. These settings can be made in the usual way, using the APC Advanced View software or using the DCE-client software, as you wrote:

...Currently, i have configured these settings by right clicking the device - netbotz appliance configuration>Alert thresholds> and selecting  sensors.

If briefly, for example, in order to receive e-mail notifications, the SMTP server must be correctly configured on your NetBotz-550 (not on the DCE-server). In addition, on your NetBotz-550 (not on the DCE-server), an e-mail notification policy must be configured, which must then be applied to the alarm threshold for a specific external sensor.

More details about this can be found in the NetBotz-4.x user manual on page Netbotz v4.x. If you have any questions, please ask.

Workaround: applicable for almost all external sensors, that are connected to the NetBotz-4.x appliance, except for discrete state sensors.

For example, let's take an external temperature sensor: in order to nothing configure on the NetBotz-4.x appliance, it is necessary in the DCE-client to create a corresponding virtual sensor for the above external temperature sensor. Then, for this virtual temperature sensor, you can create an alarm threshold in the DCE-server, apply the DCE-server notification policy for it, and check the result.

In this case, you do not need to configure the SMTP server on NetBotz-4.x appliance, you do not need to create alarm thresholds on NetBotz-4.x appliance, you do not need to create notification policies on NetBotz-4.x appliance, and you can disable the external sensor alarms on NetBotz-4.x appliance. I.e., absolutely everything is configured through a single DCE-server. It is this workaround solution, that I have been using successfully for many years ðŸ˜€.

With respect.

(CID:130099077)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:51 PM . Last Modified: ‎2024-04-05 12:06 AM

0 Likes
0
692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:51 PM . Last Modified: ‎2024-04-05 12:06 AM

Dear juice,

Have you been able to solve your problem, or do you have any more questions about it?

With respect.

(CID:130680471)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:52 PM . Last Modified: ‎2023-10-20 04:59 AM

0 Likes
0
692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:52 PM . Last Modified: ‎2023-10-20 04:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of