Adding existing alarm thresholds to newly imported devices

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Adding existing alarm thresholds to newly imported devices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
4jp
Ensign 4jp
Ensign

Posted: ‎2023-09-28 12:09 PM

0 Likes
4
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-28 12:09 PM

Adding existing alarm thresholds to newly imported devices

I should preface by saying we are still on 7.8.1 for now

 

 

Maybe I'm going about this backwards but I do not see any way of adding custom-made alarm thresholds to newly imported UPS's. It seems like you have to re-create each alarm threshold for each device you import. 


Of course I can right click --> create thresholds and have them apply to all objects in a directory, but is there no way to simply apply thresholds to individual UPS's without creating new ones?

 

Currently if I discover a new device it only gets the Communications Status threshold by default.

 

4jp_0-1695928131396.png

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2023-10-03 01:41 PM

1 Like
2
1409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-03 01:41 PM

do you mind sharing the make/model of the UPS?  If it's an APC UPS, what is the network card firmware?  You're correct that you cannot create a template or copy existing threshold alarms from an existing device to a new device.  I'm pretty sure there is a feature request for this, but if not, one can be added.

However, there may be a better solution to this issue. 
If it's an APC device, DCE should download an alarm ddf from the device that populates the device alarm tab (if you closed this, it can be opened from window->alarms->device alarms).  If the firmware is out of date or DCE is unable to download this alarm table, there will normally be an alarm that says "Device Status May be Incorrect.." https://www.apc.com/us/en/faqs/FA177004/ 

If it's a 3rd party device, it may be possible to have the DDF updated to include alarms already in the snmp mib/register map.  It's also possible that a different DDF is needed.  You can check the DDF repository here https://ddf.ecostruxureit.com/ or submit a DDF request here: https://app.ecostruxureit.com/request

Reply

Link copied. Please paste this link to share this article on your social media post.

4jp
Ensign 4jp
Ensign

Posted: ‎2023-10-04 11:11 AM

0 Likes
0
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-04 11:11 AM

We actually have very few APCs deployed currently but hope to move to an all APC environment eventually. Currently we use a mixture of mostly Vertivs, older Tripplite and Eaton devices. 

 

I have reached out to the Ecostruxure team and they said we were using the latest available DDF for Vertiv devices. 

 

Do you know if this is a feature that is available in a newer version? We plan to upgrade.... "eventually". Or could you provide more info on how to submit feature requests?

Reply

Link copied. Please paste this link to share this article on your social media post.

4jp
Ensign 4jp
Ensign

Posted: ‎2023-10-04 11:33 AM

In response to ATrabert
0 Likes
1
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-04 11:33 AM

Now that I think about it though you might be on to something, the APCs that we do have I don't think we had to configure any thresholds for. Like one of our Symmetra 40K's (fw 6.8.2) already had temp alarms, battery status, etc. configured.

 

Is it possible the Vertiv / liebert DDF still needs to be updated, even though I was told it appears to be up-to-date already? 

Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2023-10-05 04:23 AM

In response to 4jp
0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-05 04:23 AM

Do you know if this is a feature that is available in a newer version? We plan to upgrade.... "eventually". Or could you provide more info on how to submit feature requests?

 

This feature currently isn't available in your version or the latest 8.0.0.  There is a similar feature request for this already.  You can submit feature requests on this forum, via this support request page https://app.ecostruxureit.com/request, or via phone, chat, support https://www.apc.com/us/en/support/ 

In general, there is a single Liebert DDF that covers a large majority of liebert/vertiv products that ships with DCE.  Current version is 69 and available on our DDF page as just "Liebert".  I would recommend double checking the device alarms page for this device since if it's using that DDF, it should be populated.

Is it possible the Vertiv / liebert DDF still needs to be updated, even though I was told it appears to be up-to-date already? 
If you submitted a DDF request with an snmp walk/vendor snmp mib and the DDF team responded that you're using the latest DDF, then I would assume it's up to date.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of