Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:29 PM . Last Modified: 2024-04-08 01:17 AM
Hi,
Can any one help me out, I am trying to add a Cray supercomputer to DCO. Whilst I can draw the rack sizes I some how need to add these in as a power load to the PDU's does anyone have any tips for creating this custom type of load?
Many Thanks
Andy
(CID:115836920)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:30 PM . Last Modified: 2024-04-08 01:17 AM
Hi Andy
Depends on how the Cray is powered. If rack mount PDUs in the rack, then model a rack mount device. Otherwise if some other PDU, do not model a rack. Use a Powered Floor Mount device. I think u can find a generic one in the Genome Library from which u can create your custom Genomes entry. Please post your results
Cheers
Ed
(CID:115837142)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:30 PM . Last Modified: 2023-10-20 04:59 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.