Acti 9 Smartlink SI D in DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Acti 9 Smartlink SI D in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

0 Likes
5
1462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

Acti 9 Smartlink SI D in DCE

Has anyone managed to get data into DCE from a Acti 9 Smartlink SI D with PowerTags attached?

I've made a setup with 1 Acti 9 Smartlink SI D and 4 PowerTags (1541) to monitor power usage on my chillers and dry cooler. 

I started out requesting the Acti 9 Smartlink Modbus DDF file since it was supported in DCE but it didn't work. Obviously my mistake since it's a different product than the Acti Smartlink SI D πŸ˜€

After that I requested a DDF file for the exact model that I have but neerly a month went by without anything and it's driving me nuts!

So does anyone have experience with a similar setup and is willing to share with me (and everybody else) how they got it to work?`

Regards

John

(CID:132647689)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

0 Likes
0
1462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

Just an update on this topic.

The DDF for Acti 9 Smartlink SI D is out now but not working (for me). I've reported the issue on a device request so lets hope someone can fix it πŸ˜€

In the post above here I asked for another way to add a Modbus TCP device to DCE than with a DDF but I don't think thats possible at all! As i see it there is no generic Modbus TCP function/DDF where you can manualy add a Modbus register address. So I proberly just have to be a bit more patient πŸ˜€

Regards

John

(CID:132661468)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

0 Likes
0
1463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

Just an update on this topic.

The DDF for Acti 9 Smartlink SI D is out now but not working (for me). I've reported the issue on a device request so lets hope someone can fix it πŸ˜€

In the post above here I asked for another way to add a Modbus TCP device to DCE than with a DDF but I don't think thats possible at all! As i see it there is no generic Modbus TCP function/DDF where you can manualy add a Modbus register address. So I proberly just have to be a bit more patient πŸ˜€

Regards

John

(CID:132661468)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

0 Likes
0
1462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

Hi I'm trying to do this now but cant seem to get the Acti 9 Smartlink SI D DDF file to download, can you tell me where to get it please?

(CID:134689523)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

0 Likes
1
1463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

Hi James

As far as I know the right thing to do is to request the file in "Device Support". Search for the device, click it and click "I want it too".

I could also share it here πŸ˜€ schneider_acti9_smartlinksid (1).zip

I ended up taking part in the development and test of the DDF and know that there are still a few unsolved issues. Total Reactive Power, Total Apparent Power and AC Frequency are zero. The modbus registers Mounting Position (31015), Circuit Diagnostic (31016) and Breaker Rating (31017) cannot be read. These issues are no differen when I poll the registers with a modbus polling software so it might be issues with the current firmware or the documentation (wrong registers). I've been trying to find a modbus/device specialist at Schneider Electric for the last couple of months to get some help with these issues but with no luck. Still trying πŸ˜€

This is a screenshot from DCE of the working sensors on the Acti 9 Smartlink SI D.

 

Hope you find it usefull πŸ˜€

Regards

John

(CID:134689632)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

In response to DCIM_Support
0 Likes
0
1463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2024-04-04 11:30 PM

Thanks John,

Looks like still a few teething issues then. appreciate your help.

Regards

James

(CID:134689834)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2023-10-20 04:58 AM

0 Likes
0
1463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 06:31 PM . Last Modified: β€Ž2023-10-20 04:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore