ATS AP7730 high phase load

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ATS AP7730 high phase load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
8
1302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

ATS AP7730 high phase load

We have an ATS model AP7730 with a phase load reading of 45 AMPs. Both the primary and secondary input power source are 20amp circuits. NMC firmware for APP is 3.7.0 and 3.7.4 for AOS. The controller FW version is 2.0.3 with date of 9/8/10. Is this a known bug that can be resolved by FW upgrade or should the ATS be replaced.

(CID:126168014)

Labels
  • Labels:
  • DCIM Support
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

Hi Barry Patterson,

Please, share some screenshots, where you can clearly see what you are reporting. If this is the case, then with a high probability I recommend replacing this Rack ATS, as this indicates its malfunction.

If you have the time and desire, you can first just reboot the NMC of this Rack ATS: the problem may disappear. In addition, you can try completely to turn off it and turn it on again (if possible).

Further, you can update the firmware of this Rack ATS to the final version of v.3.9.2 (this is even recommended). In this case, it is very desirable to comply with all safety rules, so that IT-equipment does not lose power. But I doubt that this procedure will help fix the above mentioned problem of this Rack ATS.

With respect.

(CID:126168164)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

ATS screen shots

(CID:126170726)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:05 AM . Last Modified: ‎2024-04-05 04:16 AM

Can you see in the on-board data log where this was working for a while and then it sporadically jumped to 45 amps? (not available via the serial interface you have screenshots of if you're in there - it is available via web or FTP.) Just wondering how long it was in operation or if this happened when you powered it up.

You can try one thing first which issuing a "reset ATS Controller" command.  This can be seen in the web under Unit->Control menu or through the serial/Telnet/SSH interface, Main Menu->Device Manager->ATS Control.

Please read this first though: http://www.apc.com/us/en/faqs/FA156352 because when you do this command, the ATS output turns off very briefly for 330-340ms. Some load/equipment can ride through this and other types cannot.

If this does not work, there is not too much else you can do beyond power cycle the entire unit. I am doubtful that will work but it is free to try. 

After these suggestions, last thought is to replace it. 

(CID:126170733)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

Hi Barry Patterson,

Many thanks for the screenshots: based on the correct indication of voltages, current, power and triggered overload alarm (red LED), it's very possible that your Rack ATS is still completely functional 😀. True, it is very surprising that Rack ATS is still working with a load exceeding twice the maximum permissible for long-term operation. It is amazing!

Therefore, I would first of all be sure of what equipment is actually connected to this Rack ATS and what power does this equipment consume? Here's where to start to find out the problem with this Rack ATS.

With respect.

(CID:126170731)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

Appears this ATS has had this issue for more than 2 years. No plans to upgrade firmware due to replacement next year. 

(CID:126170737)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

Hi Barry Patterson,

I.e., I should consider that your Rack ATS is really faulty and it does not have such a big power load? I understand you correctly? Have you checked this?

With respect.

(CID:126170739)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2024-04-05 04:16 AM

Dear Barry Patterson,

Have you been able to solve this issue or not?

With respect.

(CID:126171029)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2023-10-20 04:57 AM

0 Likes
0
1301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:06 AM . Last Modified: ‎2023-10-20 04:57 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore